EagerApprentice

Greeting Learned folk
Why would you get 240v from Neutral to earth and 0v Line to Neutral? I'm getting 240 v Line to Earth.
I have around 4 fluorescent luminaires lights not working and am looking for ideas before I start fault finding.
Any help or suggestions would be greatly appreciated!
 
Hi guys Eager is a Trainee at the moment so please respect his learning curve and be gentle... I am letting this into the main forum for the moment while we sort a few things out cheers ...Darkwood!
 
Think about what potential the neutral should be at. Then think why maybe the neutral isnt at that potential.

Measuring the voltage between L-N and that should help you too.
 
If the voltage between L and E is 230v and respectively the voltage between N and E is also 230v (1ph system) then this suggest that the N is at the same potential as the L so measuring L-N will show 0v or their about.

This floating voltage on the N may be because your return to the distribution N is not connected or lost somewhere - that would be the first area to look into (broken N)
 
Remember the value you see is the potential difference between the two cables.
Because the supply voltage is 240 V (230 V) if you get this value then one of the points is at full voltage and one is at zero voltage.


The Neutral to earth is 240 V.
Therefore either the neutral or the earth is at 240 V and the earth or the neutral is at 0 V.

You have 0 V line to neutral.
This may seem that they are both at 0 V but actually it means they are both at the same voltage and there is no difference between them.

You get 240 V line to earth.
Therefore either the line or the earth is at 240 V and the earth or the line is at 0 V.

From this since earth is normally zero volts and line is normally 240 V, you can now assume that:
Earth is at zero volts
Line is at 240 V
Neutral is at 240 V

Normally Neutral is at approximately zero volts as it is earth referenced on the supply side, because the neutral is not a zero volts it is not connected to the earth reference, i.e. the neutral is disconnected from the consumer unit.
Because the neutral is at 240 V the neutral is connected to the equipment and is being raised to 240 V by the line potential via the equipment, but the equipment does not drop voltage as there is no current flow because the neutral is disconnected.
 
Remember the value you see is the potential difference between the two cables.
Because the supply voltage is 240 V (230 V) if you get this value then one of the points is at full voltage and one is at zero voltage.


The Neutral to earth is 240 V.
Therefore either the neutral or the earth is at 240 V and the earth or the neutral is at 0 V.

You have 0 V line to neutral.
This may seem that they are both at 0 V but actually it means they are both at the same voltage and there is no difference between them.

You get 240 V line to earth.
Therefore either the line or the earth is at 240 V and the earth or the line is at 0 V.

From this since earth is normally zero volts and line is normally 240 V, you can now assume that:
Earth is at zero volts
Line is at 240 V
Neutral is at 240 V

Normally Neutral is at approximately zero volts as it is earth referenced on the supply side, because the neutral is not a zero volts it is not connected to the earth reference, i.e. the neutral is disconnected from the consumer unit.
Because the neutral is at 240 V the neutral is connected to the equipment and is being raised to 240 V by the line potential via the equipment, but the equipment does not drop voltage as there is no current flow because the neutral is disconnected.
i think we have a winner here folks. Many thanks.
 

Reply to 240 between Neutral and earth but 0v between Line & Neutral in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
648
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
972
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock