His going for just 2 at moment, very little else in there gas for water, small vent. So cookers will be 93A for 2 (100% + 80%) . Not worked in many restaurants what's everyone opinions. His hoping to upgrade later on to 200A
They are 3 phase 36kw / 53A per phase, there is 8kw 3p dishwasher, 15 ceiling panel lights and sockets for display chiller units and fridge and freezers