Discuss 3 phase (220 volt) pizza oven to 1 phase (220)? in the DIY Electrical Advice area at ElectriciansForums.net

redmeat

DIY
Reaction score
0
How can I convert a 3-phase (220 volt 5.6 kw) pizza oven to 1-phase (220) 2 heating elements, no motor.

pizza oven schematics.png
 
Sorry for the late response but you would need an inverter which allows 3 phase equipment to run on single phase power.
ok Thanks.. Is there any company that you recommend or things to look for when ordering the correct one?
 
I don't see why you shouldn't connect the oven power input L1 and L2 together to one side of your 220v supply, and L3 to the other side of your 220v supply. Hopefully you have the ground connection available.

I don't think the inverter is necessary for this. The elements and transformer all appear to be 220v.
However the current draw will be approx 40 Amps, so suitable supply, cable, connector and breaker(s) needed.

I'm assuming it really is completely wired as per the diagram!
And to emphasise you would be entirely responsible for the safety of the thing having connected it differently from the manufacturers instructions. But based on the circuit diagram (unless I've missed something) this seems a possible solution.

Comments please.

And as above, sorry to have missed the original post a month ago!
 
Last edited:
I don't see why you shouldn't connect the oven power input L1 and L2 together to one side of your 220v supply, and L3 to the other side of your 220v supply. Hopefully you have the ground connection available.

I don't think the inverter is necessary for this. The elements and transformer all appear to be 220v.
However the current draw will be approx 40 Amps, so suitable supply, cable, connector and breaker(s) needed.

I'm assuming it really is completely wired as per the diagram!
And to emphasise you would be entirely responsible for the safety of the thing having connected it differently from the manufacturers instructions. But based on the circuit diagram (unless I've missed something) this seems a possible solution.

Comments please.

And as above, sorry to have missed the original post a month ago!
My bad guys I guess I had a brain fart. Sorry for the mistake on my part
 

Reply to 3 phase (220 volt) pizza oven to 1 phase (220)? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
753
I have a small mechanics shop in a rural area with no access to 3 phase. I picked up a air compressor cheap and knowing at a min. I will need a...
Replies
3
Views
2K
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
539
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
681
Hello right off the bat I'm a novice with a little better understanding than most(father was a electrician) but I am not an electrician. I'm...
Replies
26
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock