Customer has seen this on ebay, wants me to adsvise and then, if bought, install it. not done anything with electric boilers so looking for confirmation that 6.0mm 4 core on a 40A MCB, ref. method C, is about right. I calculate 33A per phase as the load. any thoughts?
ELECTRIC HEATING BOILER ELTERM "LIEUTENANT" 3 PHASES 24kW+ Digital Thermostat | eBay - https://www.ebay.co.uk/itm/ELECTRIC-HEATING-BOILER-ELTERM-LIEUTENANT-3-PHASES-24kW-Digital-Thermostat/301997800155?epid=1476045497&hash=item465078badb:g:dmQAAOSw5dlZ-kr~
 
Customer has seen this on ebay, wants me to adsvise and then, if bought, install it. not done anything with electric boilers so looking for confirmation that 6.0mm 4 core on a 40A MCB, ref. method C, is about right. I calculate 33A per phase as the load. any thoughts?
ELECTRIC HEATING BOILER ELTERM "LIEUTENANT" 3 PHASES 24kW+ Digital Thermostat | eBay - https://www.ebay.co.uk/itm/ELECTRIC-HEATING-BOILER-ELTERM-LIEUTENANT-3-PHASES-24kW-Digital-Thermostat/301997800155?epid=1476045497&hash=item465078badb:g:dmQAAOSw5dlZ-kr~
34.6Amps using 400volts Tel 33.4Amps using 415volts, just a n odd questionTel are the boilers TP&N or just TP as I have worked on boilers that only require TP no Neutral required as the elements were rate at 415volts.
 
Last edited:
bit in the real world we have 415V. suppose it depends on what voltage the manu. has used to calc. the kW.
 
it's only a (upstairs) 2 bed flat. but cust. may want to add radiators in the ground floor at a later date. better too big that too small, i reckon.
 
it's combined premises. the ground floor needs 3 phase for machinery, and it was cost effective to run all 3 phases to upstairs flat, esp. considering that a single phase electric boiler would pull close to the limit of the supply fuse.
 
it's combined premises. the ground floor needs 3 phase for machinery, and it was cost effective to run all 3 phases to upstairs flat, esp. considering that a single phase electric boiler would pull close to the limit of the supply fuse.
I thought it was, that's going to cost a lot to run, isn't it?Are they going to check the property is well insulated from heat loss?
 
it's new build, so loads of kingspan in every cavity. thing is, with a boiler this size, heat is generated faster so it's using for less time. same as a 3kW kettle draws more current than a 2kW kettle, but takes less time. cost to heat the water is the same. Kw x t.
 
it's new build, so loads of kingspan in every cavity. thing is, with a boiler this size, heat is generated faster so it's using for less time. same as a 3kW kettle draws more current than a 2kW kettle, but takes less time. cost to heat the water is the same. Kw x t.
Whenever I have been to properties with electric heating they have always moaned about the cost to use. Are you doing the whole installation Tel?
 
yep. at the moment there's just a 3 way "garage CU" supplying a double socket for power tools etc. and a 16mm 4 core from suppliers isolator ready to feed 3 phase DB. I'm in there Monday to 1st fix.
 
Whenever I have been to properties with electric heating they have always moaned about the cost to use. Are you doing the whole installation Tel?
The ones I have visited are usually cold with a portable heater in one room as they can't afford to heat the whole house. I need better situated friends than council house dwellers in Liverpool.......
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
-
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
3 phase electric boiler
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
telectrix,
Last reply from
Leesparkykent,
Replies
13
Views
7,234

Advert

Back
Top