F
fjr1300
Hi All
I’ve got to install electricity in 7 adjoining barns (10M*17M each)
Each barn will have 2*(Double waterproof Fluorescent lights) and 5 (58W) heated water troughs making a load of 438W per barn.
The loads are single phase 230V and will come from a 3 phase supply – load balancing 2 barns per phase.
The supply is around 250M away and will be underground so Method D – 4 core cable.
Now I'm not sure of which column to use on tables 4D4A and 4D4B
(Pages 280-281 17tg regs) because of the single loads but using 4 core 3 phase cables.
I'm doing the installation in France where they use non-armoured cable (less weight thank god
) (60-80cm deep in ground) but assume the armoured tables would be ok.
I obviously would not use 1.5mm cable
because the volt drop is too high and I think I'd allow for 16Amps load per phase (3680W) so that power sockets could be fitted but I'd like to see if I've got the correction factors and tables right.
I don't want to oversize the cable since the weight of 250M-300M, 4 core, is going to be fun installing
.
Thanks
Leigh
Calculations:-
Voltage = 230V
Max Voltage drop in is 4% = 9.2V
Length of Cable 300 (250M + approx middle of barns)
Required Power per barn 434 watts
Since there are 7 Barns, some of then will share the same phase
Max power, IE 2 Barns 868 Watts
Design Current 3.77 Ib Amps
Selected Breaker 5 In Amps
(Manual Selection)
Factors
1 Ca Equals 1 in 30Deg C Temp
0.65 Cg 4 Circuits (L1/L2/L3/nN)
1 Ci Equals 1 since in Ground and not Insulation involved
0.9 Cc Equals 0.9 since in ground
Cable Current Capacity 8.55 Amps It
It ≥ In / (Ca * Cg * Ci * Cc)
Select Cable size that has current capactiy ≥ to It
1.5mm
(From Table 4D4A Page 280 17th Regs)
From Table 4D4B (4) the mV/A/m) = 29 (Single phase Col 3)
Single Phase Loads
Therefore
Voltage Drop = (mV/A/m)*Ib*L / 1000 where IB=3.77 and L = 300
32.83 Vdrop
I’ve got to install electricity in 7 adjoining barns (10M*17M each)
Each barn will have 2*(Double waterproof Fluorescent lights) and 5 (58W) heated water troughs making a load of 438W per barn.
The loads are single phase 230V and will come from a 3 phase supply – load balancing 2 barns per phase.
The supply is around 250M away and will be underground so Method D – 4 core cable.
Now I'm not sure of which column to use on tables 4D4A and 4D4B

(Pages 280-281 17tg regs) because of the single loads but using 4 core 3 phase cables.
I'm doing the installation in France where they use non-armoured cable (less weight thank god
) (60-80cm deep in ground) but assume the armoured tables would be ok.I obviously would not use 1.5mm cable
because the volt drop is too high and I think I'd allow for 16Amps load per phase (3680W) so that power sockets could be fitted but I'd like to see if I've got the correction factors and tables right.I don't want to oversize the cable since the weight of 250M-300M, 4 core, is going to be fun installing
. Thanks
Leigh
Calculations:-
Voltage = 230V
Max Voltage drop in is 4% = 9.2V
Length of Cable 300 (250M + approx middle of barns)
Required Power per barn 434 watts
Since there are 7 Barns, some of then will share the same phase
Max power, IE 2 Barns 868 Watts
Design Current 3.77 Ib Amps
Selected Breaker 5 In Amps
(Manual Selection)
Factors
1 Ca Equals 1 in 30Deg C Temp
0.65 Cg 4 Circuits (L1/L2/L3/nN)
1 Ci Equals 1 since in Ground and not Insulation involved
0.9 Cc Equals 0.9 since in ground
Cable Current Capacity 8.55 Amps It
It ≥ In / (Ca * Cg * Ci * Cc)
Select Cable size that has current capactiy ≥ to It
1.5mm
(From Table 4D4A Page 280 17th Regs)
From Table 4D4B (4) the mV/A/m) = 29 (Single phase Col 3)
Single Phase Loads
Therefore
Voltage Drop = (mV/A/m)*Ib*L / 1000 where IB=3.77 and L = 300
32.83 Vdrop