W
welshmadness
Hi guys.
Installed a 63A 300mA R.C.D. on site as the eli was 5.2 ohms. (3phase tt system at a pumping station).
Anyway, when it came to the trip times, i did not get a trip at 1* current, only at 5*.(17.8ms) Is this right?
Also, what are the max tripping times for a 300mA R.C.D.?:confused:
Thanks in advance.:)
Hi
No its not Ok it should trip on 1 times the operating current, try a ramp test, to test the mA tripping current of the RCD.
Allow up to 200ms for 1 times (300mA) and 40ms for 5 times (1500mA), these are maximum operating times.
regards
Hi electro, tried the ramp test and no trip. Got a replacement unit on order so will see what happens when i fit that one.
Cheers
Absolutely correct Old Dog RCD`s up to 30ma are the only ones that are used for additional shock protection and need to operate in max 40ms at 5 times operating current.
Also the 1 times test is max 300ms for BSEN61008 and 200ms for BS4293 devices, general purposde in both cases
i am sure someone will correct me if i am wrong
you do not do a 5 times test on a 300mA rcd i wiil double check later
Hi olddog
Please read my quote no one has suggested to do a 5 x test, I suggested to a ramp test this is in no way a 5 x test, its a test of the minimum tripping current (a steady current until the unit trips). The tripping times are as per 17th edition the 5 times was to show you were the 1500mA fault current came from and expected time you should expect the unit to trip if you applied certain currents.
Hope this helps.
regards
I also believe that for BSEN 61009 it is 200ms :).