Hi guys.
Installed a 63A 300mA R.C.D. on site as the eli was 5.2 ohms. (3phase tt system at a pumping station).
Anyway, when it came to the trip times, i did not get a trip at 1* current, only at 5*.(17.8ms) Is this right?
Also, what are the max tripping times for a 300mA R.C.D.?:confused:

Thanks in advance.:)
 
Hi

No its not Ok it should trip on 1 times the operating current, try a ramp test, to test the mA tripping current of the RCD.

Allow up to 200ms for 1 times (300mA) and 40ms for 5 times (1500mA), these are maximum operating times.

regards
 
Absolutely correct Old Dog RCD`s up to 30ma are the only ones that are used for additional shock protection and need to operate in max 40ms at 5 times operating current.

Also the 1 times test is max 300ms for BSEN61008 and 200ms for BS4293 devices, general purposde in both cases
 
i am sure someone will correct me if i am wrong
you do not do a 5 times test on a 300mA rcd i wiil double check later


Hi olddog


Please read my quote no one has suggested to do a 5 x test, I suggested to a ramp test this is in no way a 5 x test, its a test of the minimum tripping current (a steady current until the unit trips). The tripping times are as per 17th edition the 5 times was to show you were the 1500mA fault current came from and expected time you should expect the unit to trip if you applied certain currents.


Hope this helps.

regards
 
Absolutely correct Old Dog RCD`s up to 30ma are the only ones that are used for additional shock protection and need to operate in max 40ms at 5 times operating current.

Also the 1 times test is max 300ms for BSEN61008 and 200ms for BS4293 devices, general purposde in both cases

I also believe that for BSEN 61009 it is 200ms :).
 

Reply to 300mA R.C.D. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
5K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Hi guys. Looking for some advice. I’ve had some building work done. 1. Outhouse. The wiring internally was changed but the wiring from the house...
Replies
7
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock