Discuss 30v on disconnected cable? in the UK Electrical Forum area at ElectriciansForums.net
Recently pulling in some new lights in my kitchen, using the original feed in I ran 2 strappers and cables for 8 downlighters.
Turned the circuit on and checked with my volt stick that the switching was correct and noticed the volt stick was going off no matter what position the switch was in.
Tested with a fluke and seen 30v to earth and neutral- even when I'd disconnected the cable?!
Can anyone shed any light on why I might be getting this voltage?
Cheers!
Probably the very high imput impedance of your tester making it too sensitive to capacitively coupled voltages.
Has your Fluke got a 'Low Z' setting?
If the cable is indeed 100% disconnected then it will be picking up a voltage by coupling from another one adjacent to it somewhere, as described above.
I went to install some spotlights in a house (owner was retired GPO spark). I was getting voltage on the earth. I couldn't understand why until I asked the owner if he had swapped any cable; he told me that he'd replaced a length from the CU to a junction box with, "a second hand, good piece". Swapped this length of cable and the fault went. I stripped the t+e in question and found the insulation of the phase had broken (repeated bending/too tight a bend) and connected with the earth.
Reply to 30v on disconnected cable? in the UK Electrical Forum area at ElectriciansForums.net
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
