Hi

I'm a mobile caterer and my unit has a 16 amp cee form inlet.

A lot of events supply a 32 amp cee form supply.

My question is if i get a 32 amp to 2 x 16 amp such as this
32_to_16amp_splitter_with_16amp_breakers_s.png
with RCD on both arms will this work. I have a support kitchen to the rear of the unit so would feed one 16 amp to the mobile unit and one to the kitchen at the rear.

Obviously i would keep each 16 amp arm to less than 3680 watts so not overloading the arms.

I've seen mentioned the 'widow maker' and hope this doesn't apply as these splitters are readily available with 2 x RCDs and assume these would trip out before any over heating?

Many thanks in advance.
 
that pic looks like its a 16A to 2 x 16A.
 
Looks alright only thing I would be concerned about is that if the supply is from a generator then I wouldn't presume that there is an earth (requires earth stake) meaning an rcd will be useless anyway
 
can't see any problems with that, except that the 32A supply will be fused accordingly, say at 32A, but your cables to the 16A sockets will most likely be rated at only 24-27A. if you have RCD protection in the van, then maybe a couple of 16A MCBs in that enclosure would be better. bear in mind that if you are a skilled person, i.e. you appreciate the dangers of electrical outlets without RCD protection, then RCD is not necessary.
 
Yeah the power would be from an onsite massive event generator, and i definitely hope that they would have the earthing issue covered.
 
Looks alright only thing I would be concerned about is that if the supply is from a generator then I wouldn't presume that there is an earth (requires earth stake) meaning an rcd will be useless anyway

WRONG. RCDs work as additional protection with or without an earthing system in place. they won't provide fault protection without eartrhing,
 
in the Van we have an MCB already for one 16 amp supply and for the support kitchen there is a multi point plug socket with an additional RCD. A bit like this

mm7BToFfoDSrEYHuUqHdHVQ.jpg
 
i'd not bother with the external RCDs then. try and find a similar unit, but without the RCDs. a couple od 20AMCBs would be better.
 