wattsup

I have to use an swa feed from a 32a single phase socket (the ip rated plastic type)

Is there a 32a plug on the market with glanding facility?

The plug will always be in, well almost always. Just unplugged for maintenance perhaps once per year.

I've used the metaflex type with cable clamp before, but not really suitable for this job.
 
I have to use an swa feed from a 32a single phase socket (the ip rated plastic type)

Is there a 32a plug on the market with glanding facility?

The plug will always be in, well almost always. Just unplugged for maintenance perhaps once per year.

I've used the metaflex type with cable clamp before, but not really suitable for this job.

by 32A socket i presume you mean a BS4343? (BS EN 60309-2)? The industrial ones?

If so, the standard ones are IP44, if you go up to an IP67 (they have the cover over the socket), they normally have a glanding facility
 
Hi shakey, glanding the socket is no problem, I need to gland the swa into the plug head.
 
Hi shakey, glanding the socket is no problem, I need to gland the swa into the plug head.

You might be able to unscrew the plug cable clamp thingy from out the end and get some reducer(s) to get you down to the size and thread you want.
Depends on what plug you get, most dont have a thread at all.

I would take it into the wholesalers and see what they can come up with.

It probably will be a PG size


You could gland your SWA into a thru box and tale the inner through a stuffing gland out the other side and into plug in normal way.
 
Could you not replace the s/o for an isolator so the supply could be locked off for maintenance?

Only saying because obviously glanding would not be a problem but also if plugs are permanently inserted the pins can corrode and fuse inside the socket causing bad connections etc.
 

Reply to 32a plug in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock