Hi there,

I need to install 4x 300W flood lights on the same circuit. What wire would you guys recommend it? What breaker size should I use?
I am asking this because customer says he had the same scenario on a different site and the lights were going dead constantly, so I have to get this install on the spot.
Regards,

Lucci
 
without getting into the are you an electrician/notifiable work debate
1200w=5.2a so if they are on their own 6a mcb and 1.0mm