Evening all

Pricing a bungalow that has 300mm insulation in the roof, as im going to be wiring around the corenrs as much as i can and through the middle would you use 4mm on the ring final circuits?

I want to use 2.5mm radials for bedrooms and living room but my boss is old school and wants to be RFC

Cheers
 
Evening all

Pricing a bungalow that has 300mm insulation in the roof, as im going to be wiring around the corenrs as much as i can and through the middle would you use 4mm on the ring final circuits?

I want to use 2.5mm radials for bedrooms and living room but my boss is old school and wants to be RFC

Cheers
Personally I'd go with radials too - for bedrooms or living rooms these days RFCs don't really add anything useful IMO - the load in an average bedroom (outside of heating or specific loads which are better run separately anyway) is tiny compared with a few years ago.

If your boss is that insistent on RFC then maybe let him do the calculation as to whether 4mm is required and swallow the additional cost. (Probably not that great tbh)

With that amount of insulation (Method 101, >100mm insulation) 2.5mm rating drops down to 17A while 4mm is 22A
 
Plus a 2.5 ring covered in insulation greater than 100 mm ( reference method 101) would not be compliant on a 32 amp ocpd as the minimum current in each leg of the ring is required to be 20 amps minimum.

If you really wanted to use 2.5mm rings then you could install them on a 20 amp ocpd.
 
Another option might be to run the 2.5mm in flexible conduit under the insulation. Should put it in ref method A, which is ok for a ring. Bit of a pain though
 
I guess it depends on the layout, lengths, etc.

Personally I would go RFC because I like the high integrity of double CPC path, and the figure of 8 test give a very good indication that everything is right. Dropping to 20A for a 2.5mm RFC is no big deal, as above the load is unlikely to be close to that in most rooms anyway.

Otherwise you are looking at 20A radial in 4mm probably, so its really a bit of personal preference or if the length is enough that VD/Zs might be a limit. The OSG has some handy tables!
 
I came across two 2.5mm final rings circuits. Both rings were independently joined in two 30A j boxes. From the j boxes the two 4mm cable went back to the CU on a 32A mcb. So each leg from the mcb had a ring off each. The 4mm was about 1.5m on each leg. The slots were all taken up, so I assume this was done to avoid fitting a new CU, which would have been difficult anyhow.
 
Evening all

Pricing a bungalow that has 300mm insulation in the roof, as im going to be wiring around the corenrs as much as i can and through the middle would you use 4mm on the ring final circuits?

I want to use 2.5mm radials for bedrooms and living room but my boss is old school and wants to be RFC

Cheers
Why use 4mm2 for RFCs when a 4mm2 radial would do just as well?
 