I quoted to go round the fence instead,
It was a new build, fcu would have fed from ring to shed with 1 double outside and one in shed with a light and this would have been 10-12 meters or so, 2 meters to shed if went under slab Ect.

Quoted £200
4 hours £120
Materials £80

He told be the previous quoted £130 all in !!

Tell the customer that your price is staying, you're too cheap as it is in my opinion, and that there is a difference between a cheap job and a good value job. Let them know exactly what paperwork they should be expecting and wait for the call, either to take you on for the job or to mop up the mess afterwards.
 
Sounds like they are just trying it on anyway. Why would a customer ring you up and say that? most just make a decision and you either get the job or never hear anything in my experience.
 
Tell the customer that your price is staying, you're too cheap as it is in my opinion, and that there is a difference between a cheap job and a good value job. Let them know exactly what paperwork they should be expecting and wait for the call, either to take you on for the job or to mop up the mess afterwards.

Yep
I said I take no short cuts and it would be to a high standard with good quality materials not thin plastic sockets Ect Ect

His face was like [emoji15] yet he was in a new 3 bed house prob £200 grand.
 
I quoted to go round the fence instead,
It was a new build, fcu would have fed from ring to shed with 1 double outside and one in shed with a light and this would have been 10-12 meters or so, 2 meters to shed if went under slab Ect.

Quoted £200
4 hours £120
Materials £80

He told me the previous quote £130 all in !!

Cash most likely, no certs, etc
 
I always try to aim for a minimum of 450mm when doing runs in gardens etc, but when its under a path... 300mm

There’s more than BS5761 to consider. Building Regulations and any applicable Housing Regulations such as NHBC might be applicable.

Good practice guides recommend:
Domestic- soft landscaping >450-600mm
Domestic- hard landscaping >600mm
Roads & driveways >900mm
Agricultural land >1000mm
Warning tape should be laid >300-450 with a 150 space between tape and cable.
Cable should be laid on a sand bed with sand covering to 100mm.
Where the cable rises above ground it should be protected by a duct, conduit or other suitable mechanical protection.
 
There’s more than BS5761 to consider. Building Regulations and any applicable Housing Regulations such as NHBC might be applicable.

Good practice guides recommend:
Domestic- soft landscaping >450-600mm
Domestic- hard landscaping >600mm
Roads & driveways >900mm
Agricultural land >1000mm
Warning tape should be laid >300-450 with a 150 space between tape and cable.
Cable should be laid on a sand bed with sand covering to 100mm.
Where the cable rises above ground it should be protected by a duct, conduit or other suitable mechanical protection.
Don't think the OP got the job or probably given up after 6 years.
 
There’s more than BS5761 to consider. Building Regulations and any applicable Housing Regulations such as NHBC might be applicable.

Good practice guides recommend:
Domestic- soft landscaping >450-600mm
Domestic- hard landscaping >600mm
Roads & driveways >900mm
Agricultural land >1000mm
Warning tape should be laid >300-450 with a 150 space between tape and cable.
Cable should be laid on a sand bed with sand covering to 100mm.
Where the cable rises above ground it should be protected by a duct, conduit or other suitable mechanical protection.

Welcome to the forum mate.
As above, best to take note of the dates of the posts.
Still its a good reference for anyone doing a search in the future.
 