joehat

I've always assumed this rule was the same under slabs or concrete, not just under soil Ect.
Am I correct as the regulation doesn't state so that's why I assumed it.

The reason being, I've just gone and quoted a job and another (electrician!!) quoted a lot less, I asked how much Ect and how he was doing it and he said he would cut a cap below the slabs and run swa to the shed. ??
 
below slabs, it's unlikely to get a spade spiked into it, so you can reduce the depth. still got to install safely and sensibly, though.
 
The requirement is to ensure that the cable will be undisturbed by any normal activity.
450mm is a generally recommended minimum and 600mm if the ground is likely to be disturbed.
However if the cable were to be laid under a fixed surface then it is protected and so long as someone can identify the warning tape before the cable if any work is done then you should be OK.
If it were under slabs then I would put a strong barrier, concrete of thick plastic capping (which would also cost a lot) in order to prevent damage on removing replacing slabs.
 
and a diversion is a detour around a flood/road works/fallen tree/road runners etc. the term you want is departure.
 
I've always assumed this rule was the same under slabs or concrete, not just under soil Ect.
Am I correct as the regulation doesn't state so that's why I assumed it.

The reason being, I've just gone and quoted a job and another (electrician!!) quoted a lot less, I asked how much Ect and how he was doing it and he said he would cut a cap below the slabs and run swa to the shed. ??
can you expand on your logical thinking here ?
 
can you expand on your logical thinking here ?
I think he means that if its under someone's rose-bed then it needs to be deep enough not to be disturbed when they dig the muck in, but if its under paving slabs then its not likely to be disturbed and if it is then it will be obvious that it is there. That's what BS7671 say's isnt it?
 
Bit of a sticky one this, dont think ive ever seen or heard of any spark actually digging a 600mm trench then back filling with sand etc as per regs down the length of someones garden with a 2.5 swa to supply a garden shed, in the real world this doesnt really happen

the amount of armoured cable ive pulled out of the ground has barely been covered with top soil
 
As far as I can remember there is no actual stated depths for SWA in the BYB.

Please correct me with the reg number if this is incorrect!
 
As far as I can remember there is no actual stated depths for SWA in the BYB.

Please correct me with the reg number if this is incorrect!

Only in special locations, depths and heights are specified for buried and overhead cables. I think the cue for general buried installation where the cable is likely to be disturbed is based on this info.

I also remember seeing some industry best practice guidance once too.
 
I agree with Welchyboy, this is a sticky one. I don't see how BS7671 could give specific depths for specific locations or purposes. I will put my tin hat on and say that 600mm is quite often unrealistic and possibly unnecessary. If the average spark working in the domestic arena quoted for the amount of labour involved he would never get the job. You have to use your common sense, if you are putting a cable under a garden that is going to be dug, then it needs to be deep enough to avoid being hit by "normal" activity, but what's normal? There is always the chance that ANY underground cable is going to be struck, including DNO cables. I recently came across a gas pipe installed to a new build with no marker tape at a depth of about 200mm, so even the supply authorities can't do it properly. What about a cable running round the perimeter of a building in a gravelled 100mm gap between the wall and paving? Are we really supposed to get it down to 450mm minimum? I think not. Sometimes its better to leave it clipped to walls/fence posts at ground level so its visible. And what if it is protected with an RCD? Should we approach it in the same manner that cables concealed in walls are? It is armoured cable at the end of the day.
I have come across loads of situations where is has been buried barely below the surface, probably because the contractor involved thought "well I can't get it 600mm so sod it". BS7671 tells us it should be deep enough to avoid being disturbed by "normal" activity, but it doesn't say what that might be. Sometimes the best you can do is make sure it is marked by tape and get it as deep as is practically possible, however deep that may be and at reasonable cost.
 
Last edited:
I think he means that if its under someone's rose-bed then it needs to be deep enough not to be disturbed when they dig the muck in, but if its under paving slabs then its not likely to be disturbed and if it is then it will be obvious that it is there. That's what BS7671 say's isnt it?
Thats not the way I read the post.
 
Yet I have had a customer lately say they dug up gravel in a new build house and guess what BANG!! Straight through the armoured cable only about an inch below gravel, being the Sparks who installed the house electrics ( ************ ) being a big company it was interesting to hear!!
 
Last edited by a moderator:

Reply to 600mm swa cable depth rule in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
703
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
900
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock