Am I right in thinking that the good thing with Indy hobs is that (virtually) all the energy goes into the pan?
So presumably, they would never be run at max.

That's right they induce the heat into the cooking utensil/pan, not the surrounding glass or element. These hobs are so fast, that they can cook a fried egg to perfection before a conventional halogen hob has even started to turn the egg white, White!! They do hit max quite often, but are still subject to thermostatic control. Just everything happens that much faster!! lol!!

I'd never swop back to a gas hob now. Never had an electric hob, they were and still are totally uncontrollable, and remain hot enough to burn you for a good hour or so, after you have finished cooking. ...total waste of energy!!
 
Last edited by a moderator:
I think a 17kW cooker could probably be run on a 40/45A breaker with possibly 10mm cable (would like 16mm but think of the wiring problems and probably overkill) then you could use a 50A cooker isolator with no problems.
(If you were going to fit an isolator!!)
If the speed is the thing as from E54 then makes it even less likely to trip.
 
But it's a damned good opinion, and makes far more sense than what you're promoting!!!

I haven't promoted anything mate. My first response was purely correcting the OP. Since then I have provided nothing but factual information.

I haven't told RVM 'not' to fit an isolator, I just told him that he doesn't 'need' to fit one. He can make his own mind up I assume. My 'opinion' on this matter is worthless as it's the OP's job, not mine.

Finally, purely for the hell of it, I shall tell you that the last 'cooker' I installed was one of many going into a commercial kitchen, each item of equipment on it's own circuit, each with it's own TP plug and socket outlet and each with its own local isolation. Proof enough that my 'argument' so to speak isn't based on the work that I do or don't do but based purely on regulatory requirements.
 
There is some bumph somewhere in OSG or whatever, and it says something along the lines of "A means of isolation within 1 metre of the appliance". I remember reading it when i put my oven in a few years ago.

Cheers...............Howard
 
A interesting debate but found one quote from D Skelton hilarious, with reference to (some block head).

Also opened my eyes to getting caught up in just doing some thing because i look at it as normal practise when sometimes i could use different methods

Thanks Dave
 
An interesting thread of varied opinions which confirms to me ........ "rules are for fools or the guidance of wise men"

Each one of us can decide where we fit .........
 
I haven't promoted anything mate. My first response was purely correcting the OP. Since then I have provided nothing but factual information.

I haven't told RVM 'not' to fit an isolator, I just told him that he doesn't 'need' to fit one. He can make his own mind up I assume. My 'opinion' on this matter is worthless as it's the OP's job, not mine.

Finally, purely for the hell of it, I shall tell you that the last 'cooker' I installed was one of many going into a commercial kitchen, each item of equipment on it's own circuit, each with it's own TP plug and socket outlet and each with its own local isolation. Proof enough that my 'argument' so to speak isn't based on the work that I do or don't do but based purely on regulatory requirements.

Why not just of let it go much earlier on then, you had made you point!! Instead you've been actively trying to support the stand, on a cooker not requiring any form of local isolator. You may well have been giving ''factual'' information, but that information is based on the general inadequacies that abounds within BS7671, ...it's the very nature of what happens when you have codes, standards, and regulations books.
 
Why not just of let it go much earlier on then

Because no one would have it. People continually trying to prove me wrong. Caught hook, line and sinker you might say but at the end of the day my first response was correct and if I'm honest, I rather enjoyed watching people trying and failing to find regulations to show me up :D

Nowt wrong with a bit of controversy!
 
Because no one would have it. People continually trying to prove me wrong. Caught hook, line and sinker you might say but at the end of the day my first response was correct and if I'm honest, I rather enjoyed watching people trying and failing to find regulations to show me up :D

Nowt wrong with a bit of controversy!

That's half the problem these day's, most here seem to think that BS7671 and it's OSG's etc will always come up with a definitive answer to any query you can throw-up!! lol!!
 
Hmmm, controversy or trolling? You say tomato I say tomaato :)

Now now, it can't be considered trolling if I'm quoting regs can it. I'm not being difficult for the sake of being difficult am I? I'm merely stating a perfectly correct point. Whether or not you agree with the regs (or at least this particular section) is up to you.

That's half the problem these day's, most here seem to think that BS7671 and it's OSG's etc will always come up with a definitive answer to any query you can throw-up!! lol!!

Most of the time the BGB will! Sometimes it leaves a little to the imagination too though I agree! Still, regs are regs, love 'em or hate 'em, they're all we are obliged to work to (discounting ESQCRs EAWRs ect...) as best practice guides are merely one man's opinion to another.
 
Morning I mention induction because someone seemed surprised by the size so was explaining why there so big.
I am installing 10mm so that she can have what ever cooker she wants (takes ages for her to make her mind up) therefore going through a 63A isolator and the mcb be will be any thing between 32A to 63A. Covering all bases.
I agree that it will never pull total load so diversity isn't a problem, to get to total load you would have to have everything on full whack and god knows what you'd be cooking for that.
I've enjoyed this thread very interesting but know one every answer the original question.
 