We have a load of approximately 18.5kw ( compressor skid). There is a plan to install a dedicated socket for this machine, the cable route is yet to be finalised and One of the contractors says 16mm2 cable 100A fuse is adequate but this comes from a rule of thumb as opposed to calculation. Is this a common rule for 63A sockets ?

Thanks
 
There isnt really a "common rule" it is entirely dependant upon cable length, installation method/route, size & type of protective device, ambient temps etc etc.

Get it designed properly then come back :)
 
without knowing the length of the run, i'd say 16mm cable on a 63A breaker is closer to the mark. i assume it's 3 phase. that equates to around 30A per phase.
 
You have to base the supply on the socket outlet because it could be used for any purpose.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Anywhere
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
63A three phase socket
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Lc1,
Last reply from
Deleted member 26818,
Replies
6
Views
4,708

Advert

Back
Top