Measure the PFC ?

I rarely find I'm working on installs where it is over 6kA, but you'll find the 10kA ranges have rcbo leads that actually reach the neutral bar whereas the 6kA ones won't. ;)
 
agree with both posts above, but be careful if you are determining pfc by measurement when really close to the transformer. I.e if in a plant room containing the transformer and the board you are working on.
most test gear measures loop impedance wrong when really close to supply transformer.
 

Reply to 6ka or 10ka xxxxxxxx in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock