Discuss 6mm Main Earthing Conductor in the UK Electrical Forum area at ElectriciansForums.net
I'm looking at doing a CU change. Current main earthing and bonding conductors are both 6mm. Tails are 16mm on a 60/80 amp fuse (TNCS). ZE = 0.1 , 230v, single cable not bunched.
Looking at the regs (543.1.1) and applying the adiabatic equation (543.1.3), 6mm seems ok for main earthing conductor.
As for bonding, BPG1 states that 6mm will be ok if there is no sign of thermal damage.
It would be quite a job to replace so hoping not to.
Am I missing something glaringly obvious please? Thanks
Pre 16th Ed (15th Ed) the Regulations never quoted a minimum size for main protective bonding for TN-C-S supplies they suggested consulting the supply company, so with this in mind and assuming this is pre 16th Ed you will never know whether those conductors fulfilled the requirements of the time.
Reply to 6mm Main Earthing Conductor in the UK Electrical Forum area at ElectriciansForums.net
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
6K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...
In my flat the main earth is the cable pictured below it has 7 strands any idea what size this is? And if it would need to be upgraded for a cu...