Thats the trouble!
I think you will have to do a continuity test on each to see exactly where they go and what they do. Dont think there is an easy fix - lesson learned (or perhaps not as it was the customer who disconnected).
Just dont assume that the blue conductors in a 3core flex are always neutral!
Thanks

I have connected the wire from the pump L/N/E to the wire from the boiler L/N/E
and the heating in the house works fine

And I have also connected the switched live N & E from the UFH wiring center to the boiler and the UFH in the office runs fine

its trying to connect them both to the boiler via the relay that causes the tripping

Thanks Tim
 
And I have also connected the switched live N & E from the UFH wiring center to the boiler and the UFH in the office runs fine
In this test you did, is the wiring centre also being simultaneously powered from the office CU?
Or is the wiring centre being powered from the boiler/pump supply?

I think you'll need to draw the circuit diagram of how everything there is wired to the relay.
 
In this test you did, is the wiring centre also being simultaneously powered from the office CU?
Or is the wiring centre being powered from the boiler/pump supply?

I think you'll need to draw the circuit diagram of how everything there is wired to the relay.
Thanks Both

When the UFH wiring center is connected to the boiler using Switched Live/N/E the supply to the wiring center is from the office CU via a 3 Amp FCU

When the boiler is connected to the house via the L/N/E from the pump which is by the boiler in the office this supply is from the CU in the house

I do not have a picture of relay wiring as this had all been disconnected to prevent the house CU from constantly tripping

What I need to understand is how to connect both locations, via the relay so that they both turn on the boiler without affecting each other

Thanks Tim
 
I do not have a picture of relay wiring as this had all been disconnected to prevent the house CU from constantly tripping

What I need to understand is how to connect both locations, via the relay so that they both turn on the boiler without affecting each other
OK, I see. Are you saying all or some of the relay wiring is no longer connected to the relay base (socket)?
 
Thanks

Yes these tests were both connecting each location separately without the relay
I'm really struggling to understand exactly what you are describing but...

IF I understand it correctly AND IF the house pump doesn't need to run for the UFH to operate AND the boiler only has a single 3 core cable (ie: it doesn't have a permanent feed and an enable) then this MIGHT BEa solution:

1764032449360.png

The pink stars being earth and neutral joints.
Earth wire from house is questionable. If all of the plumbing is in metal pipe then the house and office earths may already be linked, if not metal I'd be inclined to leave them isolated.


However as has already been mentioned the blues may not all be neutral making the above completely wrong.
 
i didn't un wire it this was done by the customer as every time the UFH came on it was tripping the consumer unit in the main house
So you have only got the customers word that it ever did work independently?
Perhaps it never has! Is the summer house/office a recent addition that has never worked as the customer now wants?
 
I'm really struggling to understand exactly what you are describing but...

IF I understand it correctly AND IF the house pump doesn't need to run for the UFH to operate AND the boiler only has a single 3 core cable (ie: it doesn't have a permanent feed and an enable) then this MIGHT BEa solution:

View attachment 124056

The pink stars being earth and neutral joints.
Earth wire from house is questionable. If all of the plumbing is in metal pipe then the house and office earths may already be linked, if not metal I'd be inclined to leave them isolated.


However as has already been mentioned the blues may not all be neutral making the above completely wrong.
Thanks

House pump is separate to the UHF and only circulates from the house rads etc

UHF has its own pump, the boiler has a three core cable (no enable or switched live) which appears to have be energized via the supply from the house pump when the CH controls in the house are operated

Thanks Tim
 
So you have only got the customers word that it ever did work independently?
Perhaps it never has! Is the summer house/office a recent addition that has never worked as the customer now wants?
Hi ,

Apparently it has been working fine until it started tripping out the CU in the main house

Thanks Tim
 
Hi Tim
Does the UFH system have a thermostat/programmer to demand heat when it's needed in the office, rather than relying on the house programmer to say when it should be on?

If it does, Sunray in post #23 gives a good solution, assuming the conditions mentioned are met.

I'm slightly concerned about the loose/detached? base of the old relay in your pic. Does it look OK? If not might be worth replacing, e.g.
 
Last edited:
the boiler has a three core cable (no enable or switched live)
If the boiler only has a 3c cable to it, it will be a basic boiler which requires a switched live, neutral and earth, not a permanent live. (unless it is intended to run 24/7 and only control is from its own internal thermostat).
 
Hi Tim
Does the UFH system have a thermostat/programmer to demand heat when it's needed in the office, rather than relying on the house programmer to say when it should be on?

If it does, Sunray in post #23 gives a good solution, assuming the conditions mentioned are met.

I'm slightly concerned about the loose/detached? base of the old relay in your pic. Does it look OK? If not might be worth replacing, e.g.

assuming this is how the house works independantly:
View attachment 124059and how UFH heating works independantly:

View attachment 124058

Then my earlier attempt ought to be a solution
Hi Sunray
this is exactly how i have connected them independently and they both work fine
Avo

Hi Avo

yes the the UFH has 3 stats (3 separate rooms in the office) that operate via the wiring center to turn on the pump & the boiler as normal

It doesn't need input from the house programmer

I have already got a replacement 8 pin relay & base, just didn't want to damage it by wiring it incorrectly

Thanks Tim


assuming this is how the house works independantly:
View attachment 124059and how UFH heating works independantly:

View attachment 124058

Then my earlier attempt ought to be a solution
 