spiderstar

i am running a 25mm swa buried then suspended if i am correct the max load allowed is 99 amp
is there a 80A spsn disconnecter about or does the wylex 110m have a interchangable fuse
the disconnecter has to be able to allow a swa to be glaneded and terminnated in
 
You tell us 99amps but dont show us how you arrived at it, confirm what spsn means is that a single pole switch +N? meaning a single phase supply, a switch disconnector dosn't have a fuse its just an isolation switch, please re-write your OP with more info and correct terminology so we could possibly help, ps .... Fused isolators, switch disconnecters etc will allow the general cabling glands for the rating of the unit so a 100amp fused isolator should be comfortable with a gland for a swa 35mm^2 or sometimes even 50mm^2 or they really wouldn't sell any.
 