S

Spudnik

Chaps,

Did a brand new install a couple of years ago...

Clients are getting a "pulsing tingle" from the metal sink in the kitchen, which they are assuming is a shock.

ALL CH and water pipework is plastic, even from the main incoming, so no MEB was connected, although was installed to the incoming location.

The only gas pipe is a feed to the combi in the kitchen at the end of the units.

Any ideas before i blast over there tomorrow?

Must admit i have never had this problem anywhere before..

Ta.
 
Chaps,

Did a brand new install a couple of years ago...

Clients are getting a "pulsing tingle" from the metal sink in the kitchen, which they are assuming is a shock.

ALL CH and water pipework is plastic, even from the main incoming, so no MEB was connected, although was installed to the incoming location.

The only gas pipe is a feed to the combi in the kitchen at the end of the units.

Any ideas before i blast over there tomorrow?

Must admit i have never had this problem anywhere before..

Ta.

When was the sink installed, could they have caught a cable when drilling?

If there's a new kitchen that would be my first theory!
 
Waste disposal unit???

Do they have a mains water supply or pumped from a well???

Any sort of pond equipment???
 
Last edited by a moderator:
Check if any potential difference between the sink and the Met
Check the resistance between the sink and the Met
Insulation resistance test of the installation

The only thing common between the sink and the electrical system seems to be the water itself
As suggested,dishwashers,washing machine,central heating boiler etc would be the favourite
Another suggestion is a cable damaged by screwing to the wall which may be close to the sink and the effects felt at the best conducting part which may be the sink top
,
 
Had a similar one Staff saying she was getting SHOCKS manager put it down to static n didnt report it I was there one day n she yelped then asked me whats causing it I held NoContact tester in stream of water n it Buzzed Confused.com traced cables from over sink water heater to FCU right through mirror fixing holes removed screws one was all black Found out by pulling cable out that First screw had gone through earth cutting it second one had gone through live and earth putting voltage to the earth this along with a faulty RCBO caused her to get a wee shock ( Company dont test RCBOS monthly)
 
I'd go with a damaged cable. Last year I had a similar problem in a kitchen. The plumber leant down to turn the stop cock off, at the same time he had his other hand on the wall to balance himself, when he touched the stopcock he got thrown across the kitchen. I checked and rechecked bonding etc, no problems. Eventually found that if i turned off a certain set of lights the problem went away.

The problem was found to be a screw put in to hold the angle bead on the corner of the wall had gone into the switch cable. It only came to light (excuse the pun) because the plumber had the lights on when it happened.

Cheers..........Howard
 
I'd go with a damaged cable. Last year I had a similar problem in a kitchen. The plumber leant down to turn the stop cock off, at the same time he had his other hand on the wall to balance himself, when he touched the stopcock he got thrown across the kitchen. I checked and rechecked bonding etc, no problems. Eventually found that if i turned off a certain set of lights the problem went away.

The problem was found to be a screw put in to hold the angle bead on the corner of the wall had gone into the switch cable. It only came to light (excuse the pun) because the plumber had the lights on when it happened.

Cheers..........Howard

is he alright now:D
 
Hi nick,

Blimey, this was over a year ago and i cant even remember what i did yesterday!!!!

From memory, i think it was down to the washing machine which had a fault.

I didnt end up going to the property as it spilled it guts that night and was disconnected, which then cleared the 'fault'.
 
I think it was one of my earliest threads on here: Tingle on anything bonded, turned out to be an electric fence energiser in a neighbouring field back-feeding through the TT! But I'd start with the more likely damaged cables first.
 
The shock could be cause by either an elevated potential at the sink itself or on the floor in close proximity. I agree as said above the most likely is a screw or fixing having clipped a cable. I would try to set up a tester to see the voltage and localise to a particular circuit first.

Had a similar fault many years ago with a shower that was caused by a tape joint buried below the screed just outside the shower pan that had been there for probably 20 years. I located it by making the floor damp with a hand sprayer and taking voltage readings to a trailing earth lead. The tester readings were a little vague ranging for about 20 - 75 volts but it was surprisingly accurate to within a couple of inches.
 