I
ianphilip007
so you can feed a (63a/30ma rcd/ 45a MCB shower cu) from a 80amp fused tails?
thankyou guitarist thats what i was thinking, so would you agree that as the shower cu can only draw 40amps the shower CU 63a/30ma rcd switch is adequate ?? no need to replace with a 80a/30ma
by backfusing Lenny are you saying that the cable feeding the shower CU (if under 3 meters) is protected by the MCB in the shower CU lets say 40amps for a 8.5KW shower.