Discuss Additional sockets & lighting. in the UK Electrical Forum area at ElectriciansForums.net
Why would a special location make any difference ?
Special location would mean it being notifiable work to LABC either direct or through CPS
Agreed I meant in addition to the cert/sBut it has no effect on the certification required. 2 minor works or 1 EIC, as Murdoch says.
Are you an Electrician? yes, then you should know the answer, A MNWC is issued for an alteration to an existing circuit, which sound's as though that's the one you require.If 4 sockets have been added to an existing ring & 2 lights have been added to an existing lighting circuit.
What certificate should be issued ?
Why not use 1 of theseMinor works x 2
Or
1 x eic
Why not use 1 of these
http://www.wmjoiner.co.uk/download/4 - Minor Works Certificate 17th Edition BS7671.pdf
Can't see why you would issue an EIC for alterations of an existing circuit.
Appendix G OSG
G2.1 The EIC is intended to be issued where more significant work is undertaken:
A complete rewire
Rewire of an existing installation
Replacement of a CU
Addition of a new circuit from the DB or CU
G2.2
MEIWC
A MEIWC is intended to be issued for an addition or alteration to an existing circuit
Adding a lighting point
Adding sockets to an existing RFC
Rerouting an existing circuit
Replacing an existing shower
Replacing circuit breakers with RCBOs where there is a difference of over current type.e,g, replacing type C for type B.
You can get MEIWC for up to 3 circuitsThat's 'cos those pesky schemes, have cotton on to the fact, that when using their on-line certification, if you've modified more than circuit, you'll need to complete more than one of their MEIWC (each cert' has only space for one circuit).
So the cost conscious amongst us, will then use an EIC, completing details for the necessary circuits, and adding 'Not Worked On' for the remainder.
Clever them schemes
Mind you, if was just two circuits or possibly 3, I'd submit 3 separate on-line MEIWC's and too hell with the cost.
You can get MEIWC for up to 3 circuits