I have been asked by a client if I can install a 2-way DB in an External Lucy cabinet for a double socket, but the only power is from an existing lighting column.
I have serious doubts about this and also what certification is required i.e minor works from column to DB as uts a alteration, then an Electrical Installation cert for a socket fed from the DB.
 
Last edited by a moderator:
You say the "only power" is coming from an existing lighting column - not quite sure what you mean by this? What is the feed to this "column"?
 
Lighting column is fed from a DB 200m away and the client doesnt want a dig the car park up.
 
what size cable and what OCPD ?
 
OK so fit your CU to the end of the SWA, then a 16A for the socket and a 6A for the existing light. up the 16A at source to 20A or 32A if Zs will allow.

edit: a EIC should suffice.
 