Bes...i`v had to do this before....when i had to take a feed from the meterbox to a C/U in a kitchen using an armoured clipped direct to an outside wall...and into the kitchen that way....
if its gettin it into the meterbox....you could cut a bit of the wall away at the edge of the meterbox.....to allow the SWA to get into the meterbox.....kind of fly it in like...
 
I would use 2 core SWA (25mm) and use the Steal armor as the Main Earth at each end terminate into a metal clad box and come from there with a 16mm earth to the CU (one end) and DNO supply (on other end). If using 3 core SWA (25mm) then run the 3rd wire as the earth and terminate that into the box as well as an additional earth to the Steal Armour. Either way the Steal Armour needs to be earthed.
 
Im terminating swa into a wiska box then from box to isolator already fitted by dno in flexible conduit to get around the double insulated part.
 