Ziggy1971

Good evening all I am new to this so apologies for not playing by the rules so I'll start again

I was asked to look at an installation for a friend who had just had a new water heater installed the installer came from the DB with a 2.5 flex and terminated into a fused spur.

In my opinion this is bad practice and I advised that she would not get a certificate with this circuit ? Was I right
 
I have asked you a question on your other thread . Why do you think this dies not comply?
 
In my opinion a flex straight from the db slung across the false ceiling does not comply, not working in the domestic sector is it normal for a flex to be used for a radial circuit ?
 
I was after some advice, I've had a look in the on site guide and apart from having no mechanical protection and it complies with volt drop earthing size it just does not feel right using flex for power circuits
 
You have been given advice, now what reg numbers or page numbers in the OSG do you think makes it wrong?

Maybe then we can help a bit more.
 
I was hoping to get in touch with a sparks who deals with this sort. Of thing on a daily basis
 
So basically you cant be bothered too look up in the BGB for info and just expect to be spoon fed it as and when you require it?
 
Last edited by a moderator:
I'd say that pretty much sums him up. Go and post on the DIY forum next. Or better still go and look in the regs and then tell me where and if it says it doesn't comply. Then advice will be given!
 
Hi Ziggy , and welcome to the forum !
Depending on the type of installation this work was completed on , I would say it was within regs all be it possibly a little rough in my opinion , if that helps !?
 
You have been given advice, now what reg numbers or page numbers in the OSG do you think makes it wrong?

Maybe then we can help a bit more.

I think you're being a bit hard here matey!

OP - there is nothing per se that prohibits you from using flex, it's just impractical due to expense. So long as the minimum conductor size and Zs are complied with, CPD rated for the cable, it's all good to go. A bit naff, maybe, but nothing 'wrong'. If you wanted to be REALLY PICKY you could possibly make an argument over whether the stranded cable has been made off into ferrules (526.9).
 