Discuss AFDDs are a massive fraud in the UK Electrical Forum area at ElectriciansForums.net
Yes it's a prevalent strategy here Vortigern...slow a process as it may be....
a daily affair for most sparks here.....
The size of those terminals !
(Have torque "wrenches" been specified yet ?
What widget exists? What are you referring to here? Your posts are like riddles sometimes.
And if arcing is the result of heated connections, then surely a device which detects this arcing is a good thing? Note, I am not necessarily saying that AFDDs do this successfully, that is a different argument.
try this DPG>
~S~
Was just required in the 2017 NEC
110.14 (D)
(D) Installation. Where a tightening torque is indicated as a
numeric value on equipment or in installation instructions
provided by the manufacturer, a calibrated torque tool shall be
used to achieve the indicated torque value, unless the equipment
manufacturer has provided installation instructions for
an alternative method of achieving the required torque.
Assuming it doesn't catch fire first... At the end stage the tempratures are already obscene.
What started AFCIs in the United States:
  • KeepingPace-37.pdf
  • KeepingPace-15.pdf
  • KeepingPace-7.pdf
Reply to AFDDs are a massive fraud in the UK Electrical Forum area at ElectriciansForums.net
Page 337 cites UL testing, where arc resistance was found to be only 30 milliohms...
Iv been given the scenario: 6 circuit earth fault loop impedance values were recorded. Each circuit has type B cb. referring to the maximum...