sparc

Got called back to a customer who'd just had kitchen fitters in, about 2 months after I'd installed a new dual RCD CU. My testing on the CU install had shown nothing massively problematice. Good Zs throughout installation.

The customer was getting a buzz when touching the sink and new dish washer or washing machine. Not a belt - just an unpleasant "tingling shock".

It turns out the customer has connected a 4-way extension block in place of existing single socket (which was spurred from above). This meant machines could be plugged in, without going to trouble of having a double socket installed. A standard (10AX) 1-gang light switch was used in place of the single socket to provide a connection point. New slimline socket faceplates had been put in by the kitchen fitters.

I measured voltage between sink and the case of each machine and got around 110V...

I checked earth loop at one of the sockets on the extension block and didn't get a reading. Checked again on double socket above work surface and got respectable reading. Opening up the double socket I could see the cpc for the spur was only connected to box, not to ring cpc. Fixed that, and replaced light switch with Wagos and blanking plate, clipping new 2.5 to sockets. Tested again and got Zs close to original readings from CU install. Checked for potential drop between machine cases and sink - zero.

I checked a number of other newly installed sockets in kitchen and found these had no earth loop either ....

Anyway, what I can't get my head around where the 110V was coming from, and what further testing to do. I measured earth leakage on main earth and bonds and found nothing greater than 8-10mA. The RCD on that circuit ramp tested to 21mA.

What am I missing - got the feeling it's something obvious!
 
If earths have not been connected it could be induced voltage on the affected earth to confirm take your long extention reel lead (if you have one and connect it to a good earth at the CU the measure between this cable and the sink then the bodies of the waching machine(s) just to confirm this is the case then sort all the wiring out make sure you have a good earth and check again I get a lot of this on lighting circuits with lLV transformer on them and no earth
 
Many thanks, oldtimer! That's interesting what you say about the LV transformers, as I raised with the customer my concern that the kitchen fitter had also wired under-cupboard lighting straight from ring circuit - no FCU - In fact, the new kitchen is pretty much an FCU no go area! Does the 110V make sense to you? It seems strangely close to half mains voltage, but I can't figure out what would split it - or it could be just coincidence?
 
Many thanks, oldtimer! That's interesting what you say about the LV transformers, as I raised with the customer my concern that the kitchen fitter had also wired under-cupboard lighting straight from ring circuit - no FCU - In fact, the new kitchen is pretty much an FCU no go area! Does the 110V make sense to you? It seems strangely close to half mains voltage, but I can't figure out what would split it - or it could be just coincidence?

Yep it makes sense to me I have mentioned this before and have measured 70-100-200vac via my fluke multimeter but if you put a voltage tester on it then it no show I had this when a customer switched on the kettle and lights at the same time he said he did not get it all the time because it was a plastic switch with metal screws

Forgot to mention I take it you had these lights on whilst investigating so if this was the case do a measure between the sink and washers with the lights on and off. Also did you by any chance use a multimeter.?
 
The customer is torn between paying me to do it, and getting the K.F. back to sort out. So I'm not getting much time on site, but enough to be getting worried about an number of aspects of the kitchen work. I was measuring voltage with my Megger, but customer had his own DMM and got pretty much same on that. I remember the lights had been on when I did the initial test and got the voltage, but don't recall them being on after I fixed earth - the possible connection with lights hadn't occurred to me. I'll need to check back to see if voltage re-appears with lights on. Thanks again!
 
Fine but mind get back to us to say how it was resolved as too many times we never get to hear the the final result
 
Well, customer says he's sorted it after getting the fitter back in. He'd tested machine cases to sink with lights on before doing that and got zero P.D. So unfortunately I've not had a chance to look at the undercupboard LV lights that are fed off the socket ring ... .unless he has further problems and decides to get me back in. Thanks for the suggestion - very helpful.
 
Did the KF also supply the client with an installation certificate and notification to the LABC?
 
As I understand it, the KF put in new cupboards and new faceplates on the sockets, cooker switch, etc. but didn't move any circuits about or extend them. As a couple of sockets appear to have been left without cpc connected I seriously doubt KF was in position to test.

By coincidence I got called to another 'refurb' yesterday - heating wasn't working - and other problems - following extensive remodelling and redecoration of the property. As all the socket plates had been replaced I asked owner if they'd been tested - obvious answer was 'no' so I ran round checking Zs - found two where no connection to cpc and two that were loose. A non-functioning socket shaver was fed from a dead cable that disappeared under the newly tiled wet room floor ....
 