S
sparc
Got called back to a customer who'd just had kitchen fitters in, about 2 months after I'd installed a new dual RCD CU. My testing on the CU install had shown nothing massively problematice. Good Zs throughout installation.
The customer was getting a buzz when touching the sink and new dish washer or washing machine. Not a belt - just an unpleasant "tingling shock".
It turns out the customer has connected a 4-way extension block in place of existing single socket (which was spurred from above). This meant machines could be plugged in, without going to trouble of having a double socket installed. A standard (10AX) 1-gang light switch was used in place of the single socket to provide a connection point. New slimline socket faceplates had been put in by the kitchen fitters.
I measured voltage between sink and the case of each machine and got around 110V...
I checked earth loop at one of the sockets on the extension block and didn't get a reading. Checked again on double socket above work surface and got respectable reading. Opening up the double socket I could see the cpc for the spur was only connected to box, not to ring cpc. Fixed that, and replaced light switch with Wagos and blanking plate, clipping new 2.5 to sockets. Tested again and got Zs close to original readings from CU install. Checked for potential drop between machine cases and sink - zero.
I checked a number of other newly installed sockets in kitchen and found these had no earth loop either ....
Anyway, what I can't get my head around where the 110V was coming from, and what further testing to do. I measured earth leakage on main earth and bonds and found nothing greater than 8-10mA. The RCD on that circuit ramp tested to 21mA.
What am I missing - got the feeling it's something obvious!
The customer was getting a buzz when touching the sink and new dish washer or washing machine. Not a belt - just an unpleasant "tingling shock".
It turns out the customer has connected a 4-way extension block in place of existing single socket (which was spurred from above). This meant machines could be plugged in, without going to trouble of having a double socket installed. A standard (10AX) 1-gang light switch was used in place of the single socket to provide a connection point. New slimline socket faceplates had been put in by the kitchen fitters.
I measured voltage between sink and the case of each machine and got around 110V...
I checked earth loop at one of the sockets on the extension block and didn't get a reading. Checked again on double socket above work surface and got respectable reading. Opening up the double socket I could see the cpc for the spur was only connected to box, not to ring cpc. Fixed that, and replaced light switch with Wagos and blanking plate, clipping new 2.5 to sockets. Tested again and got Zs close to original readings from CU install. Checked for potential drop between machine cases and sink - zero.
I checked a number of other newly installed sockets in kitchen and found these had no earth loop either ....
Anyway, what I can't get my head around where the 110V was coming from, and what further testing to do. I measured earth leakage on main earth and bonds and found nothing greater than 8-10mA. The RCD on that circuit ramp tested to 21mA.
What am I missing - got the feeling it's something obvious!