The Ghost

Strange day, changed DB in shop couple of weeks ago from old wylex with cooked neutrals and burnt out neutral bus. Wiring was the usual sargasso sea of cables above suspended ceiling, old circuits, redundant circuits and really bad light switch arrangement. Pulled out the switch wires (six) and re-located into grids at reachable height and so on. Fully expected to be called back for RCD problems.
Got a call regards the air con MCB popping a couple of weeks in. Thought mhmm just megger cables (SWA) and flexible control cable from outside fan to unit. Not possible as could not disconnect or access cables on outside unit. I suspect the outside fan is jamming but can't even look at it as it is inaccessible. Do not really know about air con apart from the obvious general principles. Anyone up on air con? Its a Fujitsu in suspended ceiling quite old by the looks of unit.
 
I did say he should get a service engineer in for air con as it was not my area. I only went to see if I could identify any obvious reason for the tripping in the supply cable. So he is going to get in the guy he uses.
 
Checked all around the ceiling cassette in the shop no rating plate or any model info either. The MCB does not go off straight away it may do, but then it can stay on for several minutes, then only a couple of minutes very random in timing terms.
 
Unlikely to be a fan problem because they're usually supplied via a speed control board and fused internally.

Did you check the running current?

As per Westward, if you're not familiar with HVACR kit I'd suggest trying a C or even D curve MCB, assuming the cct can make disconnect times. If problem persists hand it over to an A/C techie.
 

Reply to the thread, titled "Air con blowing 20a MCB a few weeks into box change in shop/commercial" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Air con blowing 20a MCB a few weeks into box change in shop/commercial
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
46
Unsolved
--

Advert

Thread statistics

Created
The Ghost,
Last reply from
Pete999,
Replies
46
Views
4,399

Advert

Back
Top