The Ghost

Strange day, changed DB in shop couple of weeks ago from old wylex with cooked neutrals and burnt out neutral bus. Wiring was the usual sargasso sea of cables above suspended ceiling, old circuits, redundant circuits and really bad light switch arrangement. Pulled out the switch wires (six) and re-located into grids at reachable height and so on. Fully expected to be called back for RCD problems.
Got a call regards the air con MCB popping a couple of weeks in. Thought mhmm just megger cables (SWA) and flexible control cable from outside fan to unit. Not possible as could not disconnect or access cables on outside unit. I suspect the outside fan is jamming but can't even look at it as it is inaccessible. Do not really know about air con apart from the obvious general principles. Anyone up on air con? Its a Fujitsu in suspended ceiling quite old by the looks of unit.
 
I did say he should get a service engineer in for air con as it was not my area. I only went to see if I could identify any obvious reason for the tripping in the supply cable. So he is going to get in the guy he uses.
 
Checked all around the ceiling cassette in the shop no rating plate or any model info either. The MCB does not go off straight away it may do, but then it can stay on for several minutes, then only a couple of minutes very random in timing terms.
 
Unlikely to be a fan problem because they're usually supplied via a speed control board and fused internally.

Did you check the running current?

As per Westward, if you're not familiar with HVACR kit I'd suggest trying a C or even D curve MCB, assuming the cct can make disconnect times. If problem persists hand it over to an A/C techie.
 
Older a/cs can be quite brutal on start up and of course the compressor drops in and out frequently. Best bet is to c or d curve and to max of cable capacity.
Any of the filters blocked? this can cause the compressor to work overtime, what temp does the unit produce at the evaporator outlet?
 
Is there not a DP isolation switch?
Not that I can see but can't get to outside where the outside unit is which is where all the business is like compressor and heavy duty fan.
Thanks again for the input it appears you are all spot on! I spoke to tech. dept. today for Fujitsu. They told me it is an obselete fifteen year old model and as stated by @plugsandsparks are brutal on the inrush side. I was told the initial draw is at least 61a so undersized on the 20a they recommended type C at least 25a or 30a. They also said it has probably been regassed with a substitute gas reducing the efficiency by up 30% considering age of the components and the gas is banned (R2 gas) since 2014 and re-filling it with that would attract a hefty fine/imprisonment! There was no info on the exact model but the guy seemed to know it well and was great, really chatty. So I have learnt a few things which is great. And thanks all again.
 
Not that I can see but can't get to outside where the outside unit is which is where all the business is like compressor and heavy duty fan.
Thanks again for the input it appears you are all spot on! I spoke to tech. dept. today for Fujitsu. They told me it is an obselete fifteen year old model and as stated by @plugsandsparks are brutal on the inrush side. I was told the initial draw is at least 61a so undersized on the 20a they recommended type C at least 25a or 30a. They also said it has probably been regassed with a substitute gas reducing the efficiency by up 30% considering age of the components and the gas is banned (R2 gas) since 2014 and re-filling it with that would attract a hefty fine/imprisonment! There was no info on the exact model but the guy seemed to know it well and was great, really chatty. So I have learnt a few things which is great. And thanks all again.
The only reason any refrigerant is required, is if there has been a leek in the pipework, as for the excuse replacement gas that's horse poo, the /C equipment will have been designed and set up for a particular Refrigerant, I think they are talking about R12, which has now been outlawed, almost like the garage telling you that a top up of Gas is required, more BS if the system has been installed properly the the refrigerant, should last for the life of the A/C unit, far to much BS spoken about refrigerants.
 
I do a/c , if its been re-gassed, will be probably from squirrel stock. Pressures are very low on the old stuff so a small leak can exists but take years to have an effect and they are hard to find hence many a/c engineers top up the gas. Easiest way to test it in your situation is with a thermograph temp device like the Flur, Set a/c to cold, max fan and measure temp of air coming off, anywhere between 5-10 degrees is what you want to see.
 
I do a/c , if its been re-gassed, will be probably from squirrel stock. Pressures are very low on the old stuff so a small leak can exists but take years to have an effect and they are hard to find hence many a/c engineers top up the gas. Easiest way to test it in your situation is with a thermograph temp device like the Flur, Set a/c to cold, max fan and measure temp of air coming off, anywhere between 5-10 degrees is what you want to see.
What you need is a refrigeration High and Low Pressure gauge set thermometers etc to set up an A/C system relying on temp off is a quick fix method, what people don't seem to understand is that, is that HVAC is a Trade on it's own, don't muck with it if you don't understand the dangers, and believe me it can be as dangerous as a Chippy , Plumber messing with electrical work, I was lucky I took many A/C courses, but I would never in the world consider myself a competent Fridge Mech.
 

Reply to Air con blowing 20a MCB a few weeks into box change in shop/commercial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some of the points should have been picked up by previous people doing the testing. Sounds like this is a thorough report. Not everything is...
Replies
11
Views
2K
I find with these so called 'class 2' metal light fittings which are basically class 1 fittings with a crappy supposedly double insulated joint...
    • Funny
    • Like
Replies
20
Views
3K
  • Question
get good quality ones(light bulbs)
Replies
9
Views
3K
ayjay
A
D
The only cabling that's affected is the cabling n this circuit which is new blue and brown cable so not that old at all. The rest f the house...
Replies
10
Views
4K
DonaldJ
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top