Hey all!

hope this is the right place for this type of questions!
I have a new phev coming in a couple of weeks and as such I need to get a power outlet to plug in the charging cable.

I live in an apartment building and have a private parking slot and a private storage room with its own breaker connected to my meter.
That breaker has two unused power outlets, one of which I intend to extend around 20 feet (6 meters) so that I can plug the charging cable of the phev. Or so I thought...
I was given a quote for a complete new breaker with THE EXACT SAME SPECS to the one I already have (25A 30mA single phase) to be installed near the parking slot.
Why?

can anyone help me understand or is the company I asked the quote trying to sell me unnecessary stuff?

thanks
 

Attachments

  • 74963B8C-EB65-4EFB-99E6-A7263BA1E80A.jpeg
    102.8 KB · Views: 29
  • EAE177E5-A9DD-4A25-9413-D0E5E48A175F.jpeg
    94.5 KB · Views: 30
I assume the photos show the existing board, since this is unsuitable for an electric vehicle charge point.

The rcd here is ac, you need type a at the very least
Thanks Julie,

yes it’s alternating current, but so are all power outlets. I need one closer to the car parking spot, so why can’t I move an existing one?

mto be clear, the vehicle comes with a charging cable that goes into a regular power outlet

36376CD7-4C24-4713-87D0-891412E2D02D.jpeg
 
No, the rcd is type ac, it needs to be type A and not type ac!

Not the fact it's alternating current being supplied.
Thanks again Julie :)

allow me to further clarify with a picture of the charging cable.

It receives 230v and has a control unit. The car itself converts the AC to DC.

I just need a 230v AC outlet. Am I right?

1585178132042.png
 
Thanks again Julie :)

allow me to further clarify with a picture of the charging cable.

It receives 230v and has a control unit. The car itself converts the AC to DC.

I just need a 230v AC outlet. Am I right?

View attachment 56618
The type of RCD required doesn't relate to the alternating current from your electricity supplier but rather the conditions under which it will or won't trip to provide protection.

In the UK, the regulations specify particular types of RCD for this application to ensure the RCD is not prevented from tripping by DC components saturating its tripping mechanism.

As per post #2 check with your electrician to see what type of RCD they propose fitting.

There is a good guide here:

 
The type of RCD required doesn't relate to the alternating current from your electricity supplier but rather the conditions under which it will or won't trip to provide protection.

In the UK, the regulations specify particular types of RCD for this application to ensure the RCD is not prevented from tripping by DC components saturating its tripping mechanism.

As per post #2 check with your electrician to see what type of RCD they propose fitting.

There is a good guide here:

Thank you Jim e Jib
 
Thanks again Julie :)

allow me to further clarify with a picture of the charging cable.

It receives 230v and has a control unit. The car itself converts the AC to DC.

I just need a 230v AC outlet. Am I right?

View attachment 56618

We are aware you are talking about a mode 2 connection, however the connection should be made with a dedicated standard socket outlet protected by a rcd of type A.

As stated a number of times, type ac is not suitable.

In addition, this type of connection is very slow to charge a vehicle, and is usually only used when you cannot use a proper charge point, such as when away from home.

With the car you usually also get a mode 3 cable (plug at each end, no electronic box in the cable). Since you are having the wiring added, I would suggest getting a dedicated ev charge point, they can be 16A or 32A, so 16A would suit your 25A availability, and charge much faster than the 10A associated with the mode 2 connection you are looking at using.
 

Reply to Am I being scammed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
688
We built a retirement home in the Philippines and relocated here a little less than 2 years ago from Georgia, USA. My wife is a Filipina and owns...
Replies
0
Views
1K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
970
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock