Hi.

Been reading the but around 427.1.7.

Does anyone have any idea on retrospective application?

Is this going to apply to every board change or just adapted to new builds and then as a C3 recommendation for everything else?

Given prices it's going to be a massive cost change on a board swop. Plus, I know for certain I'm going to have space issues with anything over 30 years old here in Fife.

Thoughts?
 
Until the make a single module arc fault breaker that can retro fit most boards and costs less than £50 a pop then they are a non starter imo
 
Regulation 421.1.7 has been redrafted. It is now a requirement (rather than a recommendation) to protect final circuits supplying socket-outlets and fixed current-using equipment with a rated current not exceeding 32 A by arc fault detection devices (AFDDs).

So the majority of circuits basically?

I've never looked at AFDDs before.

Do they have built in overload and RCD protection or are they an additional device?

Are they one device per consumer unit or one per circuit?
 
Regulation 421.1.7 has been redrafted. It is now a requirement (rather than a recommendation) to protect final circuits supplying socket-outlets and fixed current-using equipment with a rated current not exceeding 32 A by arc fault detection devices (AFDDs).

So the majority of circuits basically?

I've never looked at AFDDs before.

Do they have built in overload and RCD protection or are they an additional device?

Are they one device per consumer unit or one per circuit?

Those that I've seen (Crabtree & Wylex) are single module RCBOs, with AFDD incorporated.
 
Regulation 421.1.7 has been redrafted. It is now a requirement (rather than a recommendation) to protect final circuits supplying socket-outlets and fixed current-using equipment with a rated current not exceeding 32 A by arc fault detection devices (AFDDs).

So the majority of circuits basically?

I've never looked at AFDDs before.

Do they have built in overload and RCD protection or are they an additional device?

Are they one device per consumer unit or one per circuit?
MCB/RCD/AFDD combination, one per circuit, like a RCBO on steroids
 
MCB/RCD/AFDD combination, one per circuit, like a RCBO on steroids
And a price tag to match:
For comparison, the Wylex RCBOs:
 
Nobody will get board changes done when the board costs £2k on its own when they can get a BG from screwfix for £70, it's bad enough now! completely counter intuitive regulation
I see the "what price do you put on safety" comments now but I think making them mandatory is a step to far IMO especially when the AFCI's used across the pond don't appear to get good reviews as to how beneficial they really are.

I see a lot of problems on the horizon when these combined units start tripping is it an overload, is it an earth fault or is it an arc fault or is it a faulty protection device, ok it is easy to eliminate any overload but there are still 2 components within the protection device that need to be verified ok the RCD function can be tested but that leaves the AFDD function so do you swap the device or do you rewire the circuit or both, yes we are told the AFDD has it's in built function test but so does an RCD and that push button test does fail occassionally

I really feel the industry hasn't had the time or taken the time to properly evaluate the AFDD and inform and educate the trade of the pro's and con's before forcing the fitment of them. How long was the ELCB / RCD around before fitting them became the norm and was then more or less mandated

I think the AFDD is going to be a hard sell looking at the links in a previous post a 550 - 600% increase in cost for the protection devices alone is no doubt going to increase the posts on here by some customers who think the electrician who has told them they need a new CU at a cost of a few thousand pounds is ripping them off
 

Similar threads

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
Website
https://applebyelectrics.co.uk/
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Appleby Electrics

Thread Information

Title
Amendment 2 and AFDD's
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
98
Unsolved
--

Advert

Thread statistics

Created
Dave Appleby,
Last reply from
LastManOnline,
Replies
98
Views
13,883

Advert

Back
Top