Is anyone else having problems with the website? This is the only place it's letting me click on/post a message! ?
Discuss Amendment 2 and AFDD's in the UK Electrical Forum area at ElectriciansForums.net
I agree, I know alot of electrical fires are due to faulty white goods, there has been talk that it is in fact the white goods industry are pushing for us to incorporate AFDD to protect plugged in equipment.I can see some cases for them, but the cost/benefit looks very poor to me.
They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.
But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.
Maybe we should be pushing for the white goods industry to stop throwing cheaper & cheaper components into their appliances then we wouldn't have this problem!I agree, I know alot of electrical fires are due to faulty white goods, there has been talk that it is in fact the white goods industry are pushing for us to incorporate AFDD to protect plugged in equipment.
It all seems like a box ticking exercise to me, there's no data I'm aware of.
isn't that the sdame for an afci?
~S~
I can see some cases for them, but the cost/benefit looks very poor to me.
They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.
But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.
How about individual 13a sockets with Built in Arc Fault Interruption then ???
Thats what the plug top fuse is for, literally. A short in the flex will open the fuse within 3 cycles. Though anyone here can correct me on that if not so in practice.
And that is the problem, accordingly to what I've heard, committee that wrote the standards are made up manufacturers, in white goods industry.Maybe we should be pushing for the white goods industry to stop throwing cheaper & cheaper components into their appliances then we wouldn't have this problem!
A 13A fuse won't blow on an arc fault though. A fuse takes a relatively long time to open.
Installing the AFDD at the socket outlet is surely an acknowledgement that white goods are the main issueAnother difference between the UK and the USA.. UK installs AFDD in the distribution board, where as the USA favours them at outlet sockets.
I understood that an AFDD should be detecting an intermittent rapid change in current e.g. a loose connection in L or in N that is arcing (and which would likely not blow any fuse).Thats what the plug top fuse is for, literally. A short in the flex will open the fuse within 3 cycles. Though anyone here can correct me on that if not so in practice.
Then why not have them fitted to the appliance plug? They can bear the cost if they think it is important...And that is the problem, accordingly to what I've heard, committee that wrote the standards are made up manufacturers, in white goods industry.
Here is the typical plot, not as well defined as BS88 fuses:Do have a time current curve to common BS1363 fuses?
I understood that an AFDD should be detecting an intermittent rapid change in current e.g. a loose connection in L or in N that is arcing (and which would likely not blow any fuse).
A parallel L-N or L-E event will blow the fuse.
A series event without an outer screen to earth itself out to would technically require an AFDD, however, I do not believe partially severed cords are behind any number of fires. I aslo do not believe that AFDDs accurately detect dangerous arcing. Cost effective AFDDs will always be a compromise between tripping on dangerous arcing and not tripping on electronics, vacuums, drills and the like. All to often one is indistinguishable from the other and the 1.5-5 amp series current pickup is part of that compromise.
A brief L-N arc event will not rupture a 13A fuse.
From above curve, worst-case it is 0.03s at 200A PFC.This is assuming TDC180 fuses are of the same kind used in the UK.