- Reaction score
- 1,698
In that case, at least in the UK, and I imagine true for the NEC, you will need a cable rated at 100A, so if there's a fault, the breaker will protect the cable. So I think that means probably #2 or 3 AWG depending on the cable type.A 100amp breaker will be installed to feed it, just in case we end up using all of the outlets at the same time.