ISTR from an Aico event that you can have more than 12 units on a system using a mix of hardwire and radio linked units
Yes, but in total 12 radio units… be that detectors, wall mounted test buttons or radio modules in an otherwise mains powered hardwired detector- acting as a gateway between wired, and wireless
 
Yes, but in total 12 radio units… be that detectors, wall mounted test buttons or radio modules in an otherwise mains powered hardwired detector- acting as a gateway between wired, and wireless
The way it was put you could have 2 groups of radio linked equipment linked by a hardwire link thus exceeding 12 units
 
That got me thinking, if you house code eleven units to a Aico Ei450 Radiolink+ Control and Hush Switch, can you link another eleven to that unit as the twelfth, i.e. link a different eleven together and just link one of them to the switch? academic question.
Possibly not.

I see what others are saying. You can have 12 units on one house code, another 12 on a different house code, and a hardwired link inbetween… such as 2 radio module bases.
 
I thought it made no difference if the unit is hardware linked or radio linked it still has to be house coded?

Each one of the radio base's is part of the overall linking so only eleven units can be house coded, if indeed twelve is the limit.
 
How big? Was it hardwired?
I think there’s a limit of 12 units on an Aico Radiolink…
Similar to how Ferg described it. It was the limit of the Aico system. Blended mains and battery units. 1 large house the could be split into 2. family live one side in the summer to rent out the other side to tourists.
 
Just re-read this thread again and had the following thought, if the house was a set of apartments you would not hesitate to link all the alarms for each apartment together, same for a block of flats.
 