Hi there hope you can shed some light.
Ive got a cooker rated at 3.5kw
A hob at 6.4 kw

Now if i look to apply diversity to this to run a single T and E to a cooker switch the from the switch to a click double cooker connection point.


is this correct?

3.5kw =15.2 A
6.4KW = 27.8 A
TOTAL = 43 A

With diversity applied I'm looking at 10a + 30% of 43a = 22.9 a

Cable run 18 m Clipped direct therefore 6mm to cooker isolator

Any advice is greatly appreciated.
 
30% of 43a



​not quite. should be 30% of 33A ( remainder after the 10A).
 
I thought so but in the regs it says 10a +30% of full load current therefore 30% of the 43a ?? stumped me
 
where's that in the regs ( green book)?

edit. even so, 6mm on a 32A MCB , you're stilll well in. have you calculated the VD?
 
Last edited:
I thought so but in the regs it says 10a +30% of full load current therefore 30% of the 43a ?? stumped me

No it doesn't, it doesn't say anything about it in the regs. It is in the on site guide and the wording is 'the first 10A of the rated current plus 30% of the remainder of the rated current'
 
wondered why i'd not seen it in 7671.
 
Diversity for cookers takes into account the cyclical nature of the loads within that particular appliance and their co-ordination with each other. Where you have two separate appliances there will be no co-ordination between these appliances so I would tend to carry out a diversity calc for each appliance and then total.
You must also reference the manufacturer's information provided in case there are any requirements for cable type and size.
Also your cable size choice does not seem to have a bearing on your calculation.
 
1db75291fab030898fd2a7255d5b69af.jpg


This is what mine says.
 
Diversity for cookers takes into account the cyclical nature of the loads within that particular appliance and their co-ordination with each other. Where you have two separate appliances there will be no co-ordination between these appliances so I would tend to carry out a diversity calc for each appliance and then total.
You must also reference the manufacturer's information provided in case there are any requirements for cable type and size.
Also your cable size choice does not seem to have a bearing on your calculation.

Nonsense, it works just as well across multiple appliances as a single appliance. Each element in a single appliance is individually controlled exactly the same as if they were all in seperate appliances.

I had a fish and chip van at a festival last year, the total load of cooking appliances plus some downlights and fluorescents was 15KW, I worked happily on a 32A supply. My data logger recorded a max of ~30A whilst it was fully in use.
 
Ha Hha I've been trying to do that lol

so "It is in the on site guide and the wording is 'the first 10A of the rated current plus 30% of the remainder of the rated current'"

i take it as 10a plays the full load not the first 10a then remaining?

 
K your the man andy lol my baddd!!!! ha ha

so what cable size are you stating and how would you calculate it differently
is this now correct

3.5kw =15.2 A
6.4KW = 27.8 A
TOTAL = 43 A

With diversity applied I'm looking at 10a + 30% of 33a = 19.9 a
 