Please don't shoot me down on this one as I've been metal munching for the last few years on big jobs. I've got a 2kw bathroom fan heater that goes on the wall with pull cord. (Says bathroom on the box) I'm a bit unsure about wiring it. Ill use a fused switched spur but can I just come off of a ring from out side the bathroom. It won't be above the bath. Can I even put it in there. The building has and old consumer unit without rcds. Any advice would be very, very appreciated. Thanks.
 
I think you have just about hit every snag in the book there CB No RCD protection, Part P, and zones.

Yes you can spur it off the ring but as soon as your enter into the bathroom itself your looking at RCDs and the dreaded Part P

If you have the green book then in section 701 you will see the zones for 230 volt equipment, and you need to check where you in relation to this as the heater would not be allowed in any of them
 
how about if i keep it out of zones 1 and 2 would i need an rcd and if so would i be ok with a fused spur that has an rcd built in. im only going to put it in if i can get it to comply so if its still a no go thats ok but the box says "2kw bathroom fan heater". under what conditions would this be able to go in a bathroom. many thanks
 
IMO, allowed in zone 2. RCD FCU should make it compliant. with the FCU outside zones.
 
I just install walk in tubs in my bathroom and above that I have install heater fan but I am troubling with the same wiring issue. Thanks for guidance. Your ideas probably help me out.
 
As Malcolm rightly pointed out, Section 701 of the Bible is what you need to look at, tells you everything really and you can design your installation From it
 