Went to look at my mate's auntie's place today. Gritish Bass had been round and told her she had no earth so had have PME fitted and my mate wanted me to go round and make sure they weren't telling porkies as an "electrician" has been round last year and done some work.
Sure enough, no earth, and better still the aforementioned electrician had fitted an emergency stop tap to the water supply. In doing so, he had removed the only existing (4mm) bonding conductor and inserted a plastic housed motorized valve in its place, thereby removing any bonding.
I, dripping with sweat under a cupboard, and smelling what I think is a gas leak right next to the gas meter (about 5cm from CU), lean forward and my forehead touches an old incoming gas pipe and a new unbonded gas pipe.
Flashing lights in left eye and one fast recoil later, I got the meter out and measured PD of 40v between exposed and extraneous conductive bits!
wouldn't have been much but my sweaty forehead provided a nice electrolyte path.
Needless to say, all bonding in place, temp electrode in. safe house.
sheesh
Sure enough, no earth, and better still the aforementioned electrician had fitted an emergency stop tap to the water supply. In doing so, he had removed the only existing (4mm) bonding conductor and inserted a plastic housed motorized valve in its place, thereby removing any bonding.
I, dripping with sweat under a cupboard, and smelling what I think is a gas leak right next to the gas meter (about 5cm from CU), lean forward and my forehead touches an old incoming gas pipe and a new unbonded gas pipe.
Flashing lights in left eye and one fast recoil later, I got the meter out and measured PD of 40v between exposed and extraneous conductive bits!
wouldn't have been much but my sweaty forehead provided a nice electrolyte path.
Needless to say, all bonding in place, temp electrode in. safe house.
sheesh

. better safe etc