Benny_Boy

Went to look at my mate's auntie's place today. Gritish Bass had been round and told her she had no earth so had have PME fitted and my mate wanted me to go round and make sure they weren't telling porkies as an "electrician" has been round last year and done some work.


Sure enough, no earth, and better still the aforementioned electrician had fitted an emergency stop tap to the water supply. In doing so, he had removed the only existing (4mm) bonding conductor and inserted a plastic housed motorized valve in its place, thereby removing any bonding.

I, dripping with sweat under a cupboard, and smelling what I think is a gas leak right next to the gas meter (about 5cm from CU), lean forward and my forehead touches an old incoming gas pipe and a new unbonded gas pipe.

Flashing lights in left eye and one fast recoil later, I got the meter out and measured PD of 40v between exposed and extraneous conductive bits!

wouldn't have been much but my sweaty forehead provided a nice electrolyte path.

Needless to say, all bonding in place, temp electrode in. safe house.

sheesh:rolleyes:
 
No luck there Benny.

I too got a call last week where gas people had told client that he had earthing problems?

  • No earth at cooker switch.
No earth at double socket in bedroom.

Got test gear out and lo and behold just as reported by gas man? (our new pir friends?)

His flat had been re-wired in 2005 and pir label stated end of year for next test. The re-wire had just made use of existing conduit runs and also kept conduit as earth! Bad connection at cooker unit meant no earth and the socket had been wired surface ontop of an old single backbox with only the line and neutral brought out to face plate.

Gas man had insisted to client that these faults had to be rectified before they would carry out any work-hence my visit.

Is this a regular thing with gas men as this is first time I have come across them doing mini pir before they initiate work?:rolleyes:
 
British gas, comet, currys they are all having a go. Had a few calls from customers being told no earth present, high Zs even high volts etc. when new appliances been installed. Good for everyone I would have thought as it finds faults and generates work that would otherwise never have been picked up.
 
It is good as long as they do things safely, and does draw attention to serious faults. Just wondering how deep they go with tests?
Don't believe the gas man opened anything up though.
 
It's great that they're looking at this stuff, I've had a few jobs from comet and that delivering cookers where the switch is in the wrong place, they won't install the cooker etc, though I'm sure they just do that so they can knock off early!
 
I wouldn't be complaining but it sounds too good to be true. What is motivating the appliance suppliers and gas guys to do basic testing? Is there some health and safety regs that makes the responsible if they don't?
 
Had a call from a client once who said curry's wouldnt connect her new oven because half the DB was new and half was old!...it turned out to be a 16th split load and the cooker wasnt on the rcd side. As it was all surface etc I called curry's and told them there was no need for it to be on an rcd and got the old girls connection fee back.......another one(cant remember who) wouldnt connect an appliance because the Zs was >0.5 ohms......no mention of the type of earthing system/protective device etc....it was just a 0.5 ohms fits all rule!
 
Ive been to a property where BG have been in under their home care service. They left the Customer with a sheet noting problems found etc.. the only test carried out other then visual was a Zs at a random socket outlet.......

Had to source a problem with a crossed neutral and earth in a security light fitted by friend of the householder, kept causing the lighting circuit to trip RCD....
 