What do you do with the result as it's bypassing the upliftposted on another thread, this solves it at no cost with any MFT.
View attachment 90960
That is the point of testing the loop path without the RCD in the circuit. Connect the Line and PE at the extremity of the circuit and measure the earth fault loop from supply side of the RCD and open MCB of the circuit using a 2wire high current test which won't then trip the RCD and take out other circuits. Apparantly the uplift showing up in the MFT measurement is due to the way it carries out the low current test. It is not actually impedance in the earth fault loop at all. So the true Zs is Ze + (R1+R2) and uplift is purely a product inductance within the RCD being picked up by the way the MFT conducts a low current test. Of course another way of getting to the true measured Zs of a particular circuit is to measure the 'uplift' by taking a Zs reading on either side of the RCD and substracting this from the measured Zs at the extremity of that circuit.What do you do with the result as it's bypassing the uplift
Reply to Best MFT to avoid RCD uplift? in the Electrical Tools and Products area at ElectriciansForums.net
Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.
We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.