posted on another thread, this solves it at no cost with any MFT.
High current Zs test with RCD.jpg
 
There is an ongoing argument at the moment about manufacturers both those who make rcds/rcbos and mfts as they all have there own interpretation of the standards and regs...
The ECA came out with a cracker recently when they said we only need to record the type ac trip times on the schedule of test results and not type a, b etc...
Likewise lewden said their rcbos work with the standard but mfts cant test them!
Megger just pleased ignorance and came back with something about the mft having a wide range ...
Seems everybody is doing their own thing. Not sharing info due to proprietary tech etc and everybody is confused
 
my megger 1721 will test all types. just a setting to set for each. even my old (2008) 1553 can be set for AC or A types.
 
uplift may affect the test reading/s but have no effect when 240V is shoved into the circuit.
 
What do you do with the result as it's bypassing the uplift
That is the point of testing the loop path without the RCD in the circuit. Connect the Line and PE at the extremity of the circuit and measure the earth fault loop from supply side of the RCD and open MCB of the circuit using a 2wire high current test which won't then trip the RCD and take out other circuits. Apparantly the uplift showing up in the MFT measurement is due to the way it carries out the low current test. It is not actually impedance in the earth fault loop at all. So the true Zs is Ze + (R1+R2) and uplift is purely a product inductance within the RCD being picked up by the way the MFT conducts a low current test. Of course another way of getting to the true measured Zs of a particular circuit is to measure the 'uplift' by taking a Zs reading on either side of the RCD and substracting this from the measured Zs at the extremity of that circuit.
Megger say they now have now overcome the effect of uplift in their newer 1741 MFT by employing a different 3 wire lo current test process in the design. Anyone here had the opportunity to compare test results from a 1741 and other models, or between different MFTs ?
 
I see , I wasn't quite getting the point that the uplift was a phantom resistance

I have never came across the issue, I'm using an older 3 wire loop tester , I dunno
 

Reply to Best MFT to avoid RCD uplift? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
580
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
Hi everyone! Wanting to upgrade MFT, looking into the "FLUKE 1664" and the "MEGGER 1845"... Just wondering if anyone has experience with both and...
Replies
14
Views
3K
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
633
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
544

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock