We had a hybrid inverter installed.
It is 8kw capacity and connected to a battery, able to charge and provide supply from it of just below 8kw (max).
The manufacturer specified the line and mcb should be rated 1.25*the amps.
All was sized for a 63 MCB, even if 45 would be enough. a wylex RCD rated for 80A was also part of the circuit.
We then became aware (through forums) that there is a risk of the RCD solenoid burning when the current goes from inverter to consumer unit.
A bi-directional RCBO was then suggested.
They seem to be difficult to find. We were surprised as these battery systems are being installed all the time.
We hear inverters are usually wired with MCBs, is this correct?
It is 8kw capacity and connected to a battery, able to charge and provide supply from it of just below 8kw (max).
The manufacturer specified the line and mcb should be rated 1.25*the amps.
All was sized for a 63 MCB, even if 45 would be enough. a wylex RCD rated for 80A was also part of the circuit.
We then became aware (through forums) that there is a risk of the RCD solenoid burning when the current goes from inverter to consumer unit.
A bi-directional RCBO was then suggested.
They seem to be difficult to find. We were surprised as these battery systems are being installed all the time.
We hear inverters are usually wired with MCBs, is this correct?