bi-directional rcbos

We had a hybrid inverter installed.
It is 8kw capacity and connected to a battery, able to charge and provide supply from it of just below 8kw (max).
The manufacturer specified the line and mcb should be rated 1.25*the amps.
All was sized for a 63 MCB, even if 45 would be enough. a wylex RCD rated for 80A was also part of the circuit.
We then became aware (through forums) that there is a risk of the RCD solenoid burning when the current goes from inverter to consumer unit.
A bi-directional RCBO was then suggested.
They seem to be difficult to find. We were surprised as these battery systems are being installed all the time.
We hear inverters are usually wired with MCBs, is this correct?
 
The manufacturer advises it for protection from the 240V AC cable that supplies the inverter. This cable is also used by the inverter to supply the grid.

Protection from the cable doesn't really make sense as a reason for RCD protection.
The installer was suggesting surface mounting. The manufacturer advises 300ma RCD to avoid nuisance tripping.

A 300mA RCD would only be of use for fault protection, such as in a TT system, is that what you have?
300mA is not suitable for additional protection against electric shock, buried cables, bathrooms or any other area 30mA protection is required in the regs
 
Only if it also complies with the wiring regulations.
Of course. And that's why one read instruction first and then proceed with the installation.

OP - to answer your question in post 1.

No, inverters are not wired usually with MCB. They are wired as per manufacturer instruction, either through MCB without RCD, 30ma RCD or as in your case 300ma RCD.
I would suggest to rise your concerns with the installer and ask him/her to rectify things if they are not done accordingly.
 
Of course. And that's why one read instruction first and then proceed with the installation.

OP - to answer your question in post 1.

No, inverters are not wired usually with MCB. They are wired as per manufacturer instruction, either through MCB without RCD, 30ma RCD or as in your case 300ma RCD.
I would suggest to rise your concerns with the installer and ask him/her to rectify things if they are not done accordingly.
Thanks.
Just to give more background, the DNO feed in the area does not have a clean neutral, so the RCDs trip.
All we are doing is to follow manufacturer regulations, regulations, etc. As they may not align well, there are no quick answers!
For us Safety is paramount. For the electrician, it is following the regulations.
 
Thanks.
Just to give more background, the DNO feed in the area does not have a clean neutral, so the RCDs trip.

Could you expand on this a bit further as this isn't something I've heard of before.
How on earth does a neutral become unclean?
And how does anything in the DNO network cause an RCD in an installation to trip?

For us Safety is paramount. For the electrician, it is following the regulations.

For Electricians safety is also paramount.
 
Thanks.
Just to give more background, the DNO feed in the area does not have a clean neutral, so the RCDs trip.
All we are doing is to follow manufacturer regulations, regulations, etc. As they may not align well, there are no quick answers!
For us Safety is paramount. For the electrician, it is following the regulations.
You need to give us more info:
1. What is the earthing system?
2. What method was used to run the cable that feed inverter and what protection device are in place for this circuit?
3. Model of inverter?
4. What problems do you experiencing? Is it just nuisance tripping?
 