Had a similar problem before where low bay lighting would go off intermittently, then because there hot would take a while to re ignite.

Tracked the problem down to a large compacting machine that wasn't on the same DB but was on the same sub main bus bars, when the machine started it would cause a dip in the supply which was below the operating voltage of the fittings and hence them going off.

New supply from the mains to the lighting DB and problem solved...

Sent from my Xperia S using next doors WIFI.
 
there is 4 ac units supplied from the same board as the lighting i tried switching off the ac units and turning them on and putting them all on test mode to insure full capacity and no noticeable dimming took effect about 20 mins later the lights started to dip, what sort of correction unit have you in mind? transient correction unit or harmonics?
 
the first priority, as it's a bank, is to secure a huge loan at 0.5%, then consider looking at the fault.
 
if its been going on for 2 years then the bank mustnt be that bothered otherwise they'd have just swopped all the lights over for a different type.
not exactly sort of cash are they lol.
 
Lights all on the same phase on 1 board?

What else is on that 3ph board, are those the other circuits that were turned off?

What's the voltage at the board and at the lights at the time they dim, can't be 237v, that must be when they are O.K.?

Waste of time monitoring, I've tried that a few times and never got a result, you need a really high sample rate to catch anything.

It's a loose neutral to the 3ph board, but no-one's found it yet.
 
daft question... its not fitted with a light sensing device that dims the lights down when natural light is optimum etc... i have an office complex that i look after and all teh lights near the window are at dim level due to this set up... move 1-2 feet in and the next bank are at full brightness!!!??
 
Hi guys ill get straight to the point, I'm on a 3 phase system trying to resolve what many have tryed and failed over the last 2 years, the problem is compact pll lights dimming right down intermitently throught, actions taken are as followed...all other circuits switched off still problem, monetring device on incomer set up twice and left for a month and found no diffrence in voltage, voltage at ligts ok at 237v, swapped phase that circuit is fed from and still persists, tryed new light still same incoming voltage ok haven't tryed zs yet but now going to try

Be great to get this problem finaly resolved so please come forward with you're vews chers guys
Had the same problem with office lights, 55w pl-l for quite a while, still not got to the bottom of it. New installation about 4 years ago. Loads of machinery involved. Extra a/c units fitted later so may be worth looking into. Not been near for a few months (slow paying for other jobs done for them at present so a bit miffed). No doubt they will be onto me when the nights start drawing in more. If I find anything useful I'll let you know. Good luck.
 
daft question... its not fitted with a light sensing device that dims the lights down when natural light is optimum etc... i have an office complex that i look after and all teh lights near the window are at dim level due to this set up... move 1-2 feet in and the next bank are at full brightness!!!??

DALI units have a light sensor that is supposed to be situated away from the building windows and all street lights that are in a direct line of sight so that this doesn't happen, I had this at a new office building in Glasgow and the Light sensor was fitted onto the wall outside below gutter level, it got moved onto the middle of the roof next to the Air conditioning plant and the problem was sorted...
 
Is the lighting on one phase?
Are the phases balanced correctly over the whole installation?
if the lighting phase is heavily loaded (dropping the voltage down) and the other 2 phases lightly loaded, when a piece of three phase equiptment starts this will further drop the voltage on the phase that is loaded up
Difficult to explain but make sure all phases for the whole installation are balanced correctly!
 
That contactor must be favourite,how was it by-passed? Sometimes taking it out of circuit altogether is necessary with suitably sized links installed. If not,bother those neutral terminals.Good luck.
 