A submain supplying a distribution board is protected by a 30A BS3036 fuse, what is the maximum permissible design value Zs
A) 1.59ohms
B) 2.64ohms
c) 1.09ohms
d) 2.80ohms
Answers please, with your reasons why;):rolleyes::D
Morning Shakey
Hmmm I haven't got my copy of 17th with me (& havent had a good read) so this is off the top of my head.
I'd go 2.8 ohms as it's a distribution circuit so 5sec disscon time? (assuming cables are installed correctly to not require an rcd)
Go on tell me I'm wrong, should have left the good book in the van.
Morning Shakey
haven't got a copy of 17th yet but i thought all disconection times had been reduced to 0.4 seconds?:confused:
Well done EasyFox answer is actually 2.64 ohms but not far off
initially threw me this one
Table 41.1 gives disconnection times for 230V TN systems as 0.4S and 411.3.2.2 says table 41.1 should be used for final circuits not exceeding 32A
Table 41.2 is for 0.4S disconnection times (30A is 1.09 which is one of the answers)
Table 41.4 is for 5S disconnection times (30A is 2.64)
Great, thinks me, table 41.2 is 0.4 S, its a 30A fuse so 1.09 is the answer.......
until i read 411.3.2.3 " in a TN system, a disconnection time not exceeding 5 s is permitted for a distribution circuit a circuit not covered by reg 411.3.2.2"
and of course under the definition for a distibution circuit, it says "it is sometimes called a submain"
so it comes under the 5 s table even though it is less than 32A
cheeky bast*$%s!!!!!!:p:p:p
and 411.3.2.4 allows you to go to 1 s for a TT distribution circuit, instead of the 0.2 s in table 41.1;)
sat mine today
just happened to get ooh, give or take, 100 percent
thats 30 out of 30 then
Get in!!!:D
good luck with yours!!!
I passed my 16th in May 2006. Do I need to the 17th Edition now?
you need to do the 17th edition
when you do it is entirely up to you Darius
altough if you are going to start working to the 17th, as you can now, and wull have to after Jul, then naturally, you will need to know the book;)
Well, what a farce..........
Turned up in plenty of time, me and 11 others all sat ready to start online test.
Input username.............
input password..............
exam details.................
WRONG EXAM!
Someone had only gone an ordered the 2382-100 instead of 2382-20
Up we get and leave........
oh well, got to my private job a bit earlier :)
Reply to Bit of a cheeky 17th edition question...... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
4K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...