Dizzy_Maskell
Sound good, voltages 230 L to N on all phases
If you switched DB 4 on at DB4's main switch and all outgoing were switched off then all you are doing is extending DB4 supply by 1m at most and this will not adversely effect any other circuit unless their was the unlikely scenario of faulty switch or issues with the busbar.... we are either not getting the full story or this is not what happened regardless what the OP feels was the case.... i put it to him that the DB was switched on with downstream circuits already engaged.
is this local, dizzy? IIRC, you're based near to me.
Could you clarify what you mean by blue phase fluctuating, you have said in post 16 that the voltage was 230V L/N on all phases.
What was fluctuating on the blue phase and how did you notice / measure it?
The fault cannot be a neutral earth fault because nothing is switching the neutral, as you have 3 pole isolators the neutral is always connected no matter what.
Energising a bus bar that has no other connections closed on it can only perhaps generate a spark as the switch closes (though it would normally be a larger spark on opening) even though there is actually no voltage reference for the spark to jump to lets assume a transient / inductive connection to earth or such.
Any fault in relation to current on the supply side of the RCD cannot cause an RCD to trip because it cannot "see" this "fault".
Therefore we are left with an interconnection of the DBs on the load side (as you say very unlikely and even then it would have to be a neutral connection which would mean that the RCBOs would never stay closed) or an electromagnetic event that is jolting the RCBOs into tripping.
Could a small spark do that? doubtful I think so I am back to a loose connection that the small spark exacerbates to cause a jolt to the RCBOs but still seems odd on a three phase arrangement.
Thanks guys, the only thing we could think is a neutral issue and as said somehow linked to all DBs,
The poor blue phase was on another DB entirely again but think this turned out to be poor connection on the 88 fused isolator in the switch gear so unrelated.
About time you retired!
Nice one...when i go,i'll be wearing nothing but a curly-wurly :cheesy:no chance, mate. i'll die with me snickers on. lol.
Read my post above your blue ph issue was the cause not unrelated this is not a N issue!
My explanation account for the fluctuating Blue Ph ... (feed back through a 3ph load)
The rcd's tripping and explains the DB4 issue as coincidence.
Was there a motor or 3ph Tx running whether it be stand alon or in a control system?... if so then this is the route the backfeed will have taken running through the rcds to try return to N ?