Just been speaking to a neighbor who has recently had a new boiler installed.

For some reason (probably not CPS) they have not used the DP FCU that the old boiler was wired into and instead put a plug on it and used an existing double socket.

Has this been done to avoid having to issue a MWC for wiring into the existing FCU? Would this require a MWC and if so could the have been smart by disconnecting the flex from the boiler and wiring it into the new boiler thus avoiding interfering with an accessory?

Other than being shonky, is there any direct contravention of the BYB by using the plug/socket route.

My thinking is that there are Isolation and Functional Switching facilities local to the boiler and emergency Isolation by means of the DP switch(RCD) in the CU so while not ideal, and not how I would do it, it is not non-compliant.

Fire away......
 
No Idea, didn't fit it, more concerned that he's been told it's "against regs init" and want to get to the principle of the situation.

Your no too great at the whole discussion thing are you?:D:D:D
 
Doubt you will find anything specific in BS7671 but if instructions state double pole isolation a switched socket may not necessarily provide this. Better through a switched FCU or an unswitched socket so the service bod would have to remove the plug.
 
No Idea, didn't fit it, more concerned that he's been told it's "against regs init" and want to get to the principle of the situation.

Your no too great at the whole discussion thing are you?:D:D:D
What do you mean????
 
Bloke who fitted the boiler probably wasn't any good with Electrics and rather than fiddle about with an FCU he thought a plug top would be easier

My thoughts too, just want to check before saying it's alright as it is or not.

And although a bit short on the social skills, Westward does have the ultimate answer.

But why would one manufacturer say use a plug and another not, I suspect none would suggest using a plug but this doesn't really satisfy my curiosity as to why.
 
As westward10 has stated a unswitched socket and plug top or hard wired in to SFCU is the norm as stated by manufacturers instructions. What make and model is the boiler?
 
All of the instructions that I have seen dictate a double pole isolator with a contact separation of greater than 3mm, with a 3A fuse.

Now, if you pull a plug out of a socket then you will have double pole separation of a lot more than 3mm.

Also, BS7671 does list a plug and socket as one of the acceptable forms of isolation.
Table 53.4
The switch on a socket MAY NOT be acceptable, though, because some of those are single pole.
 
An 5 amp fuse is used on an oil boiler even with DPI of course it does not sound very good for either timers or zoned controls unless they are powering the double socket which is not altogether unusual. There are times especially on old boilers I am glad to see a plug because I can be 100% sure it's safe when I pull the plug.
 