I am glad to see a plug because I can be 100% sure it's safe when I pull the plug.
I wouldn't trust it. I have seen several installations where the boiler and the controls have separate isolation points.
I still check with my tester before putting me fingers in there.
 
554.3.3 the heater or boiler should be permanently fitted to the electrical supply through a dp linked switch
 
I wouldn't trust it. I have seen several installations where the boiler and the controls have separate isolation points.
I still check with my tester before putting me fingers in there.

I fully agree with you also many boilers especially boiler house and outdoor modules are fitted with frost thermostats which require a permanent live, obviously that is separate to the switched live.
Mistakes can and do happen when tradesmen assume everything is OK instead of carrying out the few tests that only take minutes but can mean the difference between going home at the end of the day or loved ones booking a half day with the undertaker for them.
 
There's nothing wrong as such with using a plug and socket for a boiler.
Not sure if the FCU is connected to the RFC, or on a separate circuit?
I would prefer a separate circuit, whether it be an FCU or plug and socket.
As far as I am aware, most MK sockets are double pole, as are many other makes.
Not sure about the 3mm contact gap.
Thou as has been pointed out, removal of the plug would provide a gap much more than 3mm.
 
Thanks all, you have confirmed my thoughts that it is might be alright but probably not.

I love electrics.....
 