Discuss Boiler Isolator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks Dartlec,
It is for rental property, 3 actually. My problem is that I retired 10 years ago and now live in France so can't get back easily to take care of things.
I worked commercial so never had experience in houses or EICR's. The 1 bedroom flats were all bought like this. I did have the CU's changed in 2 of them 5 years ago. I know the make/model of the fan so I'll write to Xpelair, see what they say.
I hear you about C2's meaning potential danger, I'm struggling to see how a plug top suppying a boiler or lack of isolator (except the breaker) on a fan is going to cause any danger :)
What do you think about his comment that 7671 having new editions changes things. By his reckoning rewirables should be getting C2's now. No? Or do they? It was always my belief (wrongly?), that if it was once in the regs you couldn't give it a C2.
Cheers,
Keith.
There are some things that were once fine according to the regs, that are now C2 - though a lot of them are related to very old methods of fusing, or wiring that is crumbling due to age - or the lack of an cpc for lighting circuits prior to 1966...
The situation with EICRs is complicated, partly because BS7671 doesn't properly address it and leaves it to 'guidance'. The testing is to current regulations, but things that are not as per current regulations are not automatically a code (There used to be a Code 4 that was dropped).
If a property was installed correctly as per regs say even 30 years ago, then there is not going to be much that should reach a C2, based on current guidance. Lack of RCD protection on sockets that might supply outdoor equipment and bathroom circuits is the main one that crops up.
Rewireable fuses are not themselves an automatic failure (Though personally they really should be gone in rental properties these days) - but boards that age often haven't had RCD protection added, which is where a C2 can reasonably be applied.
The other issue is that many flats/houses, including some done recently, do not comply with the Regs that were in place at the time... The classic example is single insulated twin and earth cores visible at downlight terminations.
Thanks for your help.
Cheers.
So......
Regarding the plug and socket for isolation. There is no issue with a socket and plug being used for isolation (except in bathrooms) however this needs to be double pole isolation. The switch on the socket is only single pole and it is very likely that when isolating the device the switch would be used rather than the plug being removed.
An unswitched socket outlet then. Coz any gas safe enginner wouldn't know to unplug the boiler. FFS.
Reply to Boiler Isolator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
6K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...