Discuss Bolted connections for busbars in the Industrial Electricians' Talk area at ElectriciansForums.net
Hello,
I was wondering if there is any information anywhere regarding busbar bolted connections?
recently working on two lots of terminations, one lapped and one clamped. I’m specifically looking for the effects of using bolts in different orientation on the same connection.
so one bolt with the head to the front and another with the nut to the front. I’ve always put them in the same way to be uniform and was wondering if installing them With no order could cause an issue?
potentially causing an issue with expansion rate? Or with pressure distribution on mating surfaces?
TIA
Providing it is very tight and the bolt a minimum of 8 mm2 IME then either way will be fine, use spring washers as well so the nut and bolts do not loosen
The only correct tightness for any bus are connection is the manufacturers recommendation. Over-tight can be just as dangerous as under-tight as the contact area of the busbars can become deformed and too small causing excess heating at joints.
use a torque wrench and set it to the correct value (it will surprise you just how much we tend to over-torque connections in general).
Only if you use the right kind of spring washer.
Split washers are next to useless, a disc spring (aka Belleville washer) would be far more appropriate for electrical connections.
thats what i woud do as it may invalidate the warranty set out by the manufactures its common sense
Reply to Bolted connections for busbars in the Industrial Electricians' Talk area at ElectriciansForums.net
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Hi, I'm looking into solutions for someone wanting potentially two ev chargers and wondered if anyone here has had experience with this. They...
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
