I need to bond metal stud work on new build houses, 4mm from socket to an upright, uprights have roof baton for noggins, then socket screwed to the baton, does the bond need access for testing at all?

I'm looking into metal noggins for continuity,i think it will be better, just wondering if supplementary bonding needs access for testing or inspecting as it will be covered by the plasterboard?

Cheers
Grand
 
HI all,

I need to bond metal stud work on new build houses, 4mm from socket to an upright, uprights have roof baton for noggins, then socket screwed to the baton, does the bond need access for testing at all?

I'm looking into metal noggins for continuity,i think it will be better, just wondering if supplementary bonding needs access for testing or inspecting as it will be covered by the plasterboard?

Cheers
Grand
Test it to see if it requires supplementary bonding
 
Is it extraneous is it an exposed conductive part…NO… no need to bond.
Someone got a shock off it , not my job but another site , a plasterboard screw went into the live and the whole wall was live , had an email from building firm to bond wall from one socket . And here I am looking for solutions , don't know if the RCD tripped or anythinging else as to what happened.
 
Not sure how you are going to bond all the metal partition pieces and ensure the connections will be accessible for inspection!

I'd be working out why the RCD didn't trip.
 
Someone got a shock off it , not my job but another site , a plasterboard screw went into the live and the whole wall was live , had an email from building firm to bond wall from one socket . And here I am looking for solutions , don't know if the RCD tripped or anythinging else as to what happened.
Regulations wise:

Unlikely that the stud work is an extraneous part (it's probably not imbedded in the ground), so doesn't need bonding. It's not part of the electrical system/equipment, so not an exposed conductive part, so doesn't need earthing. However, (other than the exceptions mentioned in 522.6.204), cables that pass through it need additional protection by 30mA RCD.

So, as what you're being asked to do is not required by the regs, I would say you can do it exactly as you see fit. I'm assuming the end result is to ensure that the protective device operates if there is a fault from live conductors to the studwork? If so, then it's earthing.
 
Thanks guys , u assumed the RCD tripped but I don't know much about it , builder rightly asked why it wouldn't trip straight away as this was a fault for about 6, months . I've been to look at a wall and can see it's not connected to the system at all and rightly so doesn't need bonding . They've asked for a bond strap from 1 socket to the track anywhere , witch sound reasonable , just wondering on the accessibility of that bond and does it need access to test . It will be all over boarded and skimmed hence no way if testing it
 
The death of Emma Shaw may be worth taking into account when deciding on whether to supplementary bond or not. I think I would at least bond to the sole plate of the stud wall if it is metal this would also bond the studs just as a bit of rear end covering. If you used something like the Walraven RSWB to mount your socket boxes then you have a direct metal bond to two of the studs and if the sole plate is metal you have got it covered.

I know the Emma Shaw case involved a number of events occurring that may not happen and never happen again but in this case they did an a life was lost
 
Last edited:
It would be difficult to bond a metal stud wall as the metal stud drops are not usually mechanically fixed, screwed or bolted to the floor or ceiling plate they rely on the plasterboard to hold it all together so even if you did just bond the floor or ceiling plate it may not have a good connection to the studs imho!
 
if the metal studding isn'tconected to earth (or anything else) ther will be no current flowso therefore no imbalance to trip the RCD, until somebody touches it snd provides the earth path.
 
if the metal studding isn'tconected to earth (or anything else) ther will be no current flowso therefore no imbalance to trip the RCD, until somebody touches it snd provides the earth path.
Agree but the imbalance still should be detected by the RCD someone completing the circuit to earth would cause that imbalance between the Live conductors
 

Reply to Bonding metal studwork, in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top