I have had a response from the IET. See below...
"Thank you for your enquiry. I am required to preface my remarks by saying that I have no authority to interpret the requirements of BS 7671:2018, Requirements for Electrical Installations, or any other British Standards, nor am I able to provide or confirm design or installation details as all the installation requirements may not be known to me. However, based on the information you have provided I hope you will find my comments helpful.
The industry guidance for classification codes for electrical installation condition reports is best practice guide 4, please see link below. It states that ‘if there are no observations in the report classified as C1, C2 or FI, it would not be reasonable to report the overall condition as unsatisfactory’. It also states ‘where only C3 observations have been recorded the overall outcome of the report can be stated as satisfactory’. "